Why alternators are rated in KVA?
Answers were Sorted based on User's Feedback
Answer / nithi
We can design the machines only for rated voltage(insulation
arrangement) & rated current(cooling arrangement,winding
thickness).
we can't predict the power factor while designing the
machine.Because,it is depending upon the load .
This is reason for why transformers & alternators
are rated in KVA.
Is This Answer Correct ? | 100 Yes | 6 No |
Answer / iamdon
Rating of an alternator or any electrical machine/apparatus
reflects its load carrying capability without
overheating.Temperature rise (major threat to insulation)
arises due to internal loss within the machine.
These internal losses include
1)Copper loss and
2)Core or Fe loss(hysterisis and eddy)
Both losses are independent of power factor.
Copper loss is directly proportionl to I*I
Core loss is function of voltage applied/genetated.
Both loss must be taken into account for rating
purpose.Which is only possible with taking VA which has
nothing to do with power factor.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 45 Yes | 12 No |
Answer / shariff
Transformers or alternators are rated in kvA not in kw/MW
bcoz its losses like hystersis or eddy current or copper
losses are depend upon the frequency or current non of them
on the pf. There is no consideration of pf for this machines
hence they are rated in kvA's.
Is This Answer Correct ? | 46 Yes | 20 No |
Answer / sohag kumar saha
Cu loss depends on current & iron loss depends on voltage.
Hence total Transformer/Alterntor loss depends on
volt-ampere(VA) and not on phase angle between voltage &
current i.e., it is independent of load power factor.That is
why, rating of transformers is in kVA & not in kW.
Is This Answer Correct ? | 18 Yes | 1 No |
Answer / goud
the corelosses depend on voltage and copper losses dependon
current .so the rating of alternator or transformer are
mentioned in kva
Is This Answer Correct ? | 11 Yes | 3 No |
Answer / nitin k
generally while designing an alternator we must consider 2 circuits:. i.e. electrical ckt.& magnetic ckt. Electrical ckt.is designed by considering current & magnetic circuit by volt. thats why rating is in kva.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / padmaja.s.
in transformers and alternators we have 2 types or
losses..those are eddy current and hysterious losses.eddy
current losses are depends on current..trese are variable
losses.and hysterious losses depends on voltage.so these
two losses are depends on current and voltage...so the
ratings of transformer and alternaters are rated in
voltampers(VA)Or KVA
Is This Answer Correct ? | 9 Yes | 6 No |
Answer / oni
cu loss of transformer/alternator depends on current and iron loss on voltage.Hence total loss depends on volt-ampere(VA) and not phase angle between voltage and current that means it is independent of load power factor. That is why rating of transformer/ alternator is in KVA and not in KW.
Is This Answer Correct ? | 2 Yes | 0 No |
difference between moore and mealy model
what is difference between multimeter and transmitter
what is mean by single phasing used for electrification in rural area of maharashtra ?
what's mean by Transient stability analysis?
WHAT IS THE SHOPE TESTING
how to calculate the size of the cable for a particular rating 3phase induction motor?
1 Answers Godrej, Megatron Solutions,
What is tan delta point of transformer?
why the Current transformers secodary is shorted to ground (In metering and Protection)
how calculate gd2 of ht motors
4 Answers Hindustan Copper Limited, Kohler India,
our factory is going under construction mean time transformer 1000 kva 2 nos &load break swithch 12 kv & 4 nos 750 kva 2 nos & 380 kva 2 nos generator to be errcted.how to arrange earth pits &how to earth connect & neutral pit how to calculate in earth bit size.
what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?
I want to ask that is there any relation between current denesity of copper and material purity. also is ther any standard which defines the standard current denesity of material.