Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why alternators are rated in KVA?

Answers were Sorted based on User's Feedback



Why alternators are rated in KVA?..

Answer / nithi

We can design the machines only for rated voltage(insulation
arrangement) & rated current(cooling arrangement,winding
thickness).
we can't predict the power factor while designing the
machine.Because,it is depending upon the load .

This is reason for why transformers & alternators
are rated in KVA.

Is This Answer Correct ?    100 Yes 6 No

Why alternators are rated in KVA?..

Answer / iamdon

Rating of an alternator or any electrical machine/apparatus
reflects its load carrying capability without
overheating.Temperature rise (major threat to insulation)
arises due to internal loss within the machine.
These internal losses include
1)Copper loss and
2)Core or Fe loss(hysterisis and eddy)
Both losses are independent of power factor.

Copper loss is directly proportionl to I*I
Core loss is function of voltage applied/genetated.

Both loss must be taken into account for rating
purpose.Which is only possible with taking VA which has
nothing to do with power factor.

Author:arbelectbit@yahoo.com

Is This Answer Correct ?    45 Yes 12 No

Why alternators are rated in KVA?..

Answer / shariff

Transformers or alternators are rated in kvA not in kw/MW
bcoz its losses like hystersis or eddy current or copper
losses are depend upon the frequency or current non of them
on the pf. There is no consideration of pf for this machines
hence they are rated in kvA's.

Is This Answer Correct ?    46 Yes 20 No

Why alternators are rated in KVA?..

Answer / sohag kumar saha

Cu loss depends on current & iron loss depends on voltage.
Hence total Transformer/Alterntor loss depends on
volt-ampere(VA) and not on phase angle between voltage &
current i.e., it is independent of load power factor.That is
why, rating of transformers is in kVA & not in kW.

Is This Answer Correct ?    18 Yes 1 No

Why alternators are rated in KVA?..

Answer / iamdon

Very well said by Nithi.

Is This Answer Correct ?    15 Yes 2 No

Why alternators are rated in KVA?..

Answer / goud

the corelosses depend on voltage and copper losses dependon
current .so the rating of alternator or transformer are
mentioned in kva

Is This Answer Correct ?    11 Yes 3 No

Why alternators are rated in KVA?..

Answer / nitin k

generally while designing an alternator we must consider 2 circuits:. i.e. electrical ckt.& magnetic ckt. Electrical ckt.is designed by considering current & magnetic circuit by volt. thats why rating is in kva.

Is This Answer Correct ?    5 Yes 1 No

Why alternators are rated in KVA?..

Answer / padmaja.s.

in transformers and alternators we have 2 types or
losses..those are eddy current and hysterious losses.eddy
current losses are depends on current..trese are variable
losses.and hysterious losses depends on voltage.so these
two losses are depends on current and voltage...so the
ratings of transformer and alternaters are rated in
voltampers(VA)Or KVA

Is This Answer Correct ?    9 Yes 6 No

Why alternators are rated in KVA?..

Answer / arijit

answer no 3 is perfect

Is This Answer Correct ?    5 Yes 2 No

Why alternators are rated in KVA?..

Answer / oni

cu loss of transformer/alternator depends on current and iron loss on voltage.Hence total loss depends on volt-ampere(VA) and not phase angle between voltage and current that means it is independent of load power factor. That is why rating of transformer/ alternator is in KVA and not in KW.

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

can we charge 3 ph power transformer delta-star wound with neutral grounded 6.6kV/415V from secondary side(415V) but with primary(6.6kV) open by dg,what are the disadvantages or losses.

1 Answers  


why the stator is not laminated in DC machines?

4 Answers  


why test lamp didn't glow across 500v megger?

4 Answers   Aurobindo,


HOW TO CALCULATE CAPACITOR BANK OR HARMONIC FILTER CALCULATION

0 Answers   ECCI, EFS,


generally in LT and MV motors we are using 3.5Coresx16,25,35,50 etc cable for supply.although motors is earthed at two point and having all protection.then why we are using that 1/2 core for earthing the motors.while in HT cable we are using only 3core cable for motor supply.generally lt and mv motors are delta connected and ht motors having star connection.whethere it is having any relation with winding connection( star or delta).all motors i am talking about are dol only.can anybody solve my confusion.thanks...

0 Answers  


voltmeter kya hota hy ?

2 Answers  


Hi,Any one has idea regarding the KPTCL Recuirtments for AE'e & JE's for the year of 2009-10???Kindly help in regards..

2 Answers  


a battery is having capacity 100AH and 25% charging .if a load taking 10A & connected 6 hour .what is the final condition of the battery.

0 Answers  


Why Diffrential and Ref relays are used together although Diffrential relay can protect Pri and Sec of Transformer

1 Answers   Qatar Gas,


what is the principle of tubelight ??? what is the function of starter and choke ???

1 Answers  


slipring induction motor starting time Lrs operating why lrs starting time lrs outer body didn't get shock

0 Answers   Ramco,


why 3phase is 440v but where as we get phase voltage 220v,we have to get 220*3=660v.can u pleas give in detailed

3 Answers   Avantha Group,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)