Answer / srinivasan.s
For 11KV line CT ratio was 1200A-600A-300A/1Amp
PT ratio was 11KV/110V
for 11KV CT's PT's minimum 3cores are available
generally 1'st core for metering
2nd and 3rd cores for protection purpose.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / khalid k usafzai
for installing cts and pts on 11 kv line first of all the load to be connected is required.then we will proceed.bye
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / shivadathathri
11 KV CTs & PTs , Out door Pedestal mounting versions will do. Current ratio , STC Rating & Insulation level can be determined with connected load. Like breaker / Transformer Etc. Example : Load is 11KV 100KVA transformer is connected . Then use 11KV Cts CTR: 5/5 Amps , Class 0.5 for metering , Class : 5p10 for Protection . OCF - 150XI nominal . Oil cooled CTs for MUSS. If it is mounted inside panel / Control room then Use Resin cast type. SHIVADATHATHRI- 9632153842.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / alternate_reality
A 100/5 Amp CTPT can be installed for metering purpose in
Indsustries...
| Is This Answer Correct ? | 2 Yes | 3 No |
which part of transformer heats up the most and why? windings, core or oil .
How many gap between finger contact in a.c.b. and v.cb.?
In a voltage-controlled current source A A current booster is never used B The load is always floated C A stiff current source drives the load D The load current equals Isc
Why the wave trap is put in Y phse only in switchyard?why not in other phases?
1 Answers IAG Automation, REL,
What is the meager?
which seven wonders are selected in india in 2008-2009
what is the earth current,reverse power,electrical trip generator short circuit,low voltage, high voltage please discribe me
what is difference between neutral and earth
what will happen if i connect the buchholz relay in reverse direction.
How much width of the land shall have to be left below the EHT line of 440 kv as per the rule. i am told that a corridor of 35 M width is to be left free below 220 kv line. please confirm
In HVDC LINE RECTIFIER CONTROL ON CONSTANT CURRENT AND INVERTER CONTROL CONSTANT EXITATION ANGLE CONTROL BUT HOW INVERTER CONTROL CONSTANT CURRENT?
what is rated current and operating current?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)