While testing the 33KV Busbar by using Hipot kit, what
should be the test voltage we have to apply
Answers were Sorted based on User's Feedback
Answer / ramaswamy venkatachalam
At the factory, it is tested by applying twice the voltage.
ie, 2U. If a dc kit is used, (2U)/sqrt(2) + 1 KV. Which is
a minimum of 48 kV. You can use 50 kV test kit for the same.
Convert the ac rms voltage to dc by dividing by sqrt(2) and
multiplying it by 2 and adding 1kV to it.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / gunaskaran
for ac 0.8(2E+1) normally we r doing in ac if customer
asking we can do the dc for DC (2E+1*1.414)0.8 this 1.414
is AC to DC conversion this for site for factory we have to
applie 100% voltage
Is This Answer Correct ? | 1 Yes | 3 No |
Even motor protection, why motor burn out ?
Pl. brief about break-down maintenance of machine tool.
before transformer oil dielectric strenght tests are taken the oil should be allowed to settle to remove option 1 air bubbles 2 gasses 3 contamination 4 water
What is the name of powder which is used in inner side of a cable? and purpose?
While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply?
What is the impact of MCCB & MPCB on Distributed Control System?
what type of motor used to move a 1 ton gate? and relate ratings with load.
what are the points to be consider for MCB(miniature circuit breaker selection?
Active power= VI COS FI But incase of leading power factor ( more than unity), may we use other formula ? because the cos fi (value of cos thita) should not be grater than one.
Why water bubbles when D.C. Current is passed through it? Why not when A.C. Current is passed?
what is the rating of Insulation tester for measure 15 KW, 3 phase 415V 50 HZ induction motor?
at what condition restricted earth fault relay will act?