Answer / carl_ellis
When you need troubleshooting assistance you need to supply
certain critical information:
1) Has the device ever worked correctly before for some
time period and then failed?
Or is this a first time commissioning issue?
2) What is the brand name and model number of the device?
3) Because all devices have an input and an output, exactly
what each is (is your sensor one thermocouple, two
thermocouples, or one RTD?)
- You do tell us the output is 21.5mA.
4) What are the error codes or what the error symptoms?
- You mention the display shows ambient temperature
5) What you've done to troubleshoot the problem, like
substitute a known source (simulator) and the result
was . . . . ?
Evaluation:
ambient temperature: A short circuit (a wire) across the
terminal inputs of a thermocouple input will display near-
to-ambient temperature, specifically the temperature of the
terminal block connectors. The value is the cold junction
compensation (CJC) temperature.
Some high end transmitters will show the CJC temperature.
Is the display stuck on the CJC temperature, rather than
its input? Is there a short across the (+) and (-) input
terminals?
21.5mA is a very common fail-safe alarm level, outside the
normal 4-20mA range, but indicating that there is a serious
fault in the transmitter setup or operation. If the fail-
safe is configured for fail high, an open input (among many
other things) could cause the fault.
Smart transmitters generate an error code and save it. If
the transmitter has HART, the error code is in one of the
diagnostics registers, but a HART communicator is needed to
access the error code.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / carl_ellis
A short circuit (both thermocouple wires touching each
other) in the thermocouple extension wire leads will create
an ambient or near-ambient temperature reading, but I am
unaware of any temp transmitter that can detect that problem
and go to fault mode at 21.5mA.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Explain level troll principle & interface level measurement.
send me model hpcl questions pleas..........my mail id mohideen.dharvesh@gmail.com
How can we calibrate pressure and flow transmitter in the field(online)?
-/5A. What is the meaning and limitations of this in energy meter constant. It is a 3 phase LT Energy Meter. If this Energy Meter is connected through a CT of ratio 200/5 Amps, then what is the multiplying constant and how its will be calculated.
draw a loop drawing of vibration beginning to end
why the positioner output is 3-15psi
yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help me fine how we can normal the broblems?
Why we use 4 - 20 ma?
why flow transmitter showing 2.2ma?
Why some transmitter shows flow in MMWC and some in TPH?
Can any one send me IOCL instrumentation question papers.. i dont know the pattern of the questions and what to prepare can any one help me on this .. my email id is anwarnishil@gmail.com
In which principles tx ,pressure gauge,Temp gauge,control valve works?
0 Answers Bajaj, Professional Instruments,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)