why temperature transmitter is showing ambienttemp.but 21.5ma.
alarm AO showing at the display &how to sloves this problem.
Answers were Sorted based on User's Feedback
Answer / carl_ellis
When you need troubleshooting assistance you need to supply
certain critical information:
1) Has the device ever worked correctly before for some
time period and then failed?
Or is this a first time commissioning issue?
2) What is the brand name and model number of the device?
3) Because all devices have an input and an output, exactly
what each is (is your sensor one thermocouple, two
thermocouples, or one RTD?)
- You do tell us the output is 21.5mA.
4) What are the error codes or what the error symptoms?
- You mention the display shows ambient temperature
5) What you've done to troubleshoot the problem, like
substitute a known source (simulator) and the result
was . . . . ?
Evaluation:
ambient temperature: A short circuit (a wire) across the
terminal inputs of a thermocouple input will display near-
to-ambient temperature, specifically the temperature of the
terminal block connectors. The value is the cold junction
compensation (CJC) temperature.
Some high end transmitters will show the CJC temperature.
Is the display stuck on the CJC temperature, rather than
its input? Is there a short across the (+) and (-) input
terminals?
21.5mA is a very common fail-safe alarm level, outside the
normal 4-20mA range, but indicating that there is a serious
fault in the transmitter setup or operation. If the fail-
safe is configured for fail high, an open input (among many
other things) could cause the fault.
Smart transmitters generate an error code and save it. If
the transmitter has HART, the error code is in one of the
diagnostics registers, but a HART communicator is needed to
access the error code.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / carl_ellis
A short circuit (both thermocouple wires touching each
other) in the thermocouple extension wire leads will create
an ambient or near-ambient temperature reading, but I am
unaware of any temp transmitter that can detect that problem
and go to fault mode at 21.5mA.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Please send the all question with answer related for interview.
What is DCS and PLC scanning time?
how its work inductive proximity sensor explain briefly?
what is controlling card in dcs? how u measure dcs memory?what is bus in dcs?how u know dcs speed n ehternet speed?
I have a problem with a valve (air to close). When it is fully closed and try to open 1% it doesn't responce till 3% open suddenly more than 3% then back to 3%. I tried to tune positioner then removed it, the problem still exist. Any idea
what is the role of proportional in process control?
what is the criteria to decide conductor size of a cable ?
Is SmartPlant Instrumentation taking advantage of the quality assurance procedures within Intergraph?
what are the different types of communication cables used in automation and what are the difference in the cables
How d.p. Transmitter can be applied to open tank?
An engineering term STALL used in compressor operation what it means?
if we open the inlet of an air regulator ,how it will affect the out put of regulator? (out put of regulator is using to operate an on-off valve.it is an air to open valve,and valve is in open position.my doubt is air regulator will hold the valve in open or not,if there is no consumption or leak in regulator out put side ,we only loose the input pressure.)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)