Why 4ma - 20ma signal used in instrumentation??
Answers were Sorted based on User's Feedback
Answer / avinash kumar
if we consider 0-20 or any other value then we can't
differentiate that this instrument has fault or this
instrument has in its minimum position.if it indicated 0
means, it has some fault, if it indicates 4 means it is in
on state having minimum position.so by this idea we can
differentiate b/w damage instrument and the minimum
position instrument.
Is This Answer Correct ? | 18 Yes | 5 No |
Answer / abhishek k sharma
1:-4ma - 20ma are used to ged know about the live zero
positon.it means that if we use 0ma then we cannot get
excect error as postioner do not gos negative values.
2:- also we have less chances of noise in 4ma to 20ma range
which help us to carry out calibration.
3:- it do not produces spack if we joints its (+)/(-) so
can be used in hazard conditions.
4:-it is idealy accepted for calibration of instruments by
all.
Is This Answer Correct ? | 6 Yes | 4 No |
Answer / sreekanth
There are some Transmitters which operate from 0 to 20 MA.
But 4-20 MA is standard.
As above one of our friend told, we cannot differentiate
whether the Instrument is fault or not when we get 0 MA.
Rather than that there is one more reason. MA will be
accurate from 3 MA. But getting exact ratio between 3 to 20
MA is bit difficult. so 4-20 MA is commonly used so that 0,
25, 50, 75, 100% can be converted in to 4- 20.
Is This Answer Correct ? | 7 Yes | 5 No |
Answer / saba anjum
we can easily find that this signal is live zero or dead
zero.
Is This Answer Correct ? | 1 Yes | 3 No |
what is the difference between two wire transmitter and 4- wire transmitter
how magentic flow tx. vortex flow tx & ultrasonic flow tx works and its prinicle?its callibtration prosedure?
What does a fire detector detects?
canu tell me why 4-20 ma and why not this 3-25ma?please give reason of this value.
types of transformer.. 1ph 3ph or core shell?
if a dp transmitter has range 100 in H2O and flow is 20mmcf and if the flow is changed to 25 mmcf then what is the formula to determine new range of transmitter
how can you change unit of totalizer in siemens mag 5000 flow meter?
How to do gas analysers calibration in AUTO and Manually by using zero and span gas?
What is protocol ?
explain Cascade Control strategy with the help of a block diagram. also exlain its working in a distillation column
What is the difference between radar and ultrasonic level transmitter? Which method is best and more accurate?
Why Flow measurement has to use Square Root