Explain the Term in CT Name Plate – Class: 5P10
Answers were Sorted based on User's Feedback
Answer / chola
CT error 5P10 It means .10 times of current fiows as per Ct
ratio the error will be 5%.
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / mriganka das
Class 0f CT : 5P10.....
It state that if there 10 times current of plug setting
flows through the primary, there would be +/- 5 % error may
take place in the secondary side of the CT.
So 5 is the tolarence or accuracy class & 10 is the
accuracy class limit factor.it is denoted by the symbol
Eeta.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / s c budhiraja
this relates to ct meant for protection purpose.5p stands
for class of ct which means the current error at rated
primary current is 1%(+or-)and 10 mean that this ct will be
reasonably accurate upto 10 times the rated primary current.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / pravin
15 VA 5P 10
accuracy limit factor = 10
accuracy class = 5P
accuracy power = 15 VA
| Is This Answer Correct ? | 1 Yes | 0 No |
It defines tat, at 10 times (During fault condition) of the
rated current of CT the accuracy shall be +/-5%.
for more, plz refer is-2705 part-1 to 4, ETD-34.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ganesan.n
5P - Accuracy Class
10 - Composite error rate accuracy limit primary current (%)
| Is This Answer Correct ? | 1 Yes | 8 No |
54 Comments Alok and Bhanu play the following min-max game. Given the expression N = 38 + X*(Y – Z) where X, Y and Z are variables representing single digits (0 to 9), Alok would like to maximize N while Bhanu would like to minimize it. Towards this end, Alok chooses a single digit number and Bhanu substitutes this for a variable of her choice (X, Y or Z). Alok then chooses the next value and Bhanu, the variable to substitute the value. Finally Alok proposes the value for the remaining variable. Assuming both play to their optimal strategies, the value of N at the end of the game would be?
how generator avr give to the input?
if a 3phase motor runnig in star delta starter with full load of its,and its rated 15 amps.now we conneted over load thermal relay at its main contactor,here what will be our amps sittings?
WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE (XLPE)?
what is the use of Antipumping in HT breakers.
A 3 phase transformer's (Y-Y) Y and B phase is (Y and B connection not broken) broken from neutral and R and Nutral connection is ok, what will be the relay tripping and why
My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there any possibility of Technical Problem ?
why grid frequency varry time to time?
What is the capacity of the Fastners 12mm?
earth also having a gravitational force (magnetic field of north and south)but it attracts any object compare to this theartifical magnetic cant perform same as earth why?
The 3 phase 400 hp 440 volt slip ring induction motor do not take one phase amps why ? The motor is running good condition
what is mcb
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)