Explain the Term in CT Name Plate – Class: 5P10
Answers were Sorted based on User's Feedback
Answer / chola
CT error 5P10 It means .10 times of current fiows as per Ct
ratio the error will be 5%.
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / mriganka das
Class 0f CT : 5P10.....
It state that if there 10 times current of plug setting
flows through the primary, there would be +/- 5 % error may
take place in the secondary side of the CT.
So 5 is the tolarence or accuracy class & 10 is the
accuracy class limit factor.it is denoted by the symbol
Eeta.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / s c budhiraja
this relates to ct meant for protection purpose.5p stands
for class of ct which means the current error at rated
primary current is 1%(+or-)and 10 mean that this ct will be
reasonably accurate upto 10 times the rated primary current.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / pravin
15 VA 5P 10
accuracy limit factor = 10
accuracy class = 5P
accuracy power = 15 VA
| Is This Answer Correct ? | 1 Yes | 0 No |
It defines tat, at 10 times (During fault condition) of the
rated current of CT the accuracy shall be +/-5%.
for more, plz refer is-2705 part-1 to 4, ETD-34.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ganesan.n
5P - Accuracy Class
10 - Composite error rate accuracy limit primary current (%)
| Is This Answer Correct ? | 1 Yes | 8 No |
Synchrounous motor is three phase motor,but its not self starting .why?
23 Answers Delta Beverages, KI, L&T, NTC, TVS, Wipro,
why the rotor current becomes in steady state during high slip region? please verify with equations.
WHAT IS SYNCHRONISING?
what the principle of sincroscope?how it works?when it needed?
What exactly is meant by harmonics and harmonic current?? and what is skewing with regard to this??
in a large three phase induction motors usually the value of full load slip is
Haw to check conductivity of budbar
on 22.03.2015 at 17:15hrs Y phase 66kV class Power Trf-2 Current transformer has flashed over and oil came out. The failed CT has been replaced on 24.03.2015 at 13:15hrs and the Trf has been charged in presence of RT Hassan after conducting the pre-commissioning tests. On the same day at 17:00hrs the commissioned CT has again flashed over and immediately the Trf has been isolated from power supply. It is confirmed the secondary is not opened and checked the earth integrity and is found ok. Here what would be the reason for the CT failure?
What type of surgery impedence with 200ohs
If I want to replace a 26KW Slip ring Motor with a Squirrel Cage motor & Drive (for a Hoist Application). How can I approximate the Motor & Drive HP required in new Setup.
why vaccum circuit breakers are preferred over m.o.c.b
Why can not you store AC power in battery like DC power?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)