if a 3phase motor runnig in star delta starter with full
load of its,and its rated 15 amps.now we conneted over load
thermal relay at its main contactor,here what will be our
amps sittings?
Answers were Sorted based on User's Feedback
Answer / pillay
If star delta connection it will have 6 wires . so the amp setting of the TOR WILL BE FULLLOAD AMPS /ROOT 3
15/1.732 =8.6 AMPS
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / k.prakashchandra
The thermal relay is coeected to mains and not after the
starter.The setting may be at 110 to 120 % 0f full
load.i.e.16 to 18 A
| Is This Answer Correct ? | 1 Yes | 4 No |
what is the function of supervison relay?Draw its wiring diagram.
2 Answers IBM, R.R. ISPAT LIMITED,
why generaotr rating is in kva and dc motor in kw?
what is mean by lookup table in microprosser.
What are the different sizes of cables for H.T and L.T side of supply?
7 Answers Bhel, BSES, Karthik Industries, Lanco, Nedco, Shilpa Electrical Engineers, TATA, Torrent Power,
watt meter have 4 terminals what there name??? and what theses 4 terminals indicates ?? and why 2 terminals are short circuited??
what is transformer?
what is the working principle of tube light?
APPLICATIONS OF SHUNT GENERATOR
What is the difference between relays and contactor construction wise?
What is the formuala to calculate the rating of motor protection circuit breaker
what is meant by LT & HT?
why any centrifugal blower draw more current in starting. consider id fan and fd fan?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)