What is maximum demand and contract demand?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
contract demand is also called billing demand and it is not
likely to be exceeded by the consumer.It is the assured
maximum demand.Max demand is the actually recorded one
during the month and the consumer will be penalized if this
exceeds the CD as per applicable rules formed by the supplier..
| Is This Answer Correct ? | 61 Yes | 9 No |
Contract demand is the demand(load in terms of KVA/MVA)
based on the customer requirement with power supplier as
per the supply agreement. Maximum demand is the maximum
load recorded during the billing cycle (usually a month)as
per the power supplier. Billing demand is the demand
charges billed by the supplier based on maximum demand
recorded and contract demand. It varies depending on the
power supplier. For example in Karnataka state all
Electricity Supply Company under Karnataka Power
Transmission Corporation, bills based on 75% of the
contract demand or maximum demand recorded whichever is
higher in a month.
| Is This Answer Correct ? | 38 Yes | 1 No |
Answer / pepepy
Contract demand is the demand where we are making contract with government that we will not cross the value of contract demand.
Maximum demand is the demand where we are utilizing the electricity maximum on a particular time period.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / harsh patel
Contract demand is the total power (KW or KVA) required by the customers and written agreement done with supplier.while maximum demand is the peak load recorded for intervals of some particular time such as 15 minute or 30 minute.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / s t gokhale
I think ,span of time for which the maximum power is used is also important while defining contract demand. In Maharashtra state, maximum demand for a continuous span span of 30 minutes is recorded in the meters and billed as contract demand.
| Is This Answer Correct ? | 0 Yes | 6 No |
how do u calculate CT rating for 10 mva transformer
For 160kw motor what size of cable and material is needed.?
A three phase transformer 460v primary 220v secondary (three phase four wire system.) Why did we get 460 volts across the neutral on the secondary side?
why spark is produced in mosquito bat?and what are the ways to reduce it?
what is the difference between induction and synchronous motor?explain in simple words?why 3 phase motor is given preference over single phase motor.
What is a Servo Stabliser.
what is standard height of an energy meter from ground?
why dont we connect the two 12 V DC batteries in parallel, for an inverter (UPS)? is there any harm ?
what is inrush curent.
Why 60Hz frequency is used in America what are all the benifits?
What should be the length of transmission line so that we can see/obtain the full sine wave of voltage??
I want to do a mini project. Now I'm studying in 6th semis tor EEE Engineering.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)