why circuit breaker closing time is always higher then
tripping / opening time.
Answers were Sorted based on User's Feedback
Answer / prabhat kumar sinha, banswara
Whenever a Loaded circuit breaker is interrupted an arc is
inevitably formed between the contacts. But in the closing
time there is no current carrying by Circuit Breaker and no
any other effect on contacts. So, circuit breaker closing
time is always higher then tripping/opening time.
| Is This Answer Correct ? | 34 Yes | 22 No |
Answer / kevin
who the hell is this latika and s. karthik. i think they are non technical or does not have any basics of electrical. the first answer is the correct one
| Is This Answer Correct ? | 14 Yes | 2 No |
Neither of you are correct and for that matter who really
cares which is greater?
The opening and closing times of circuit breakers are
based on mechanical variables such as charging spring
tension, contact gap, trip mechanism delay etc. The goal
for a circuit breaker is to make or break the contacts as
quickly as possible to either slam the device on line or
open the contacts quickly enough to minimize the time that
an arc exists at the contacts.
What is significant are two measurements that provide an
indication of what the actual operating characteristics of
the circuit breaker are.
First, connect the contacts in series with one another
and a timer such that the circuit goes timer, 1st contact
set, 2nd contact set, 3rd contact set timer. (In one out
the other). Time the opening and closing of the circuit
breaker contacts. This will provide the fastest set of
contact make/break time.
Second, connect the contacts so that they are in
parallel with eachother record the value (This is the
average open/close time).
Once you have done this several times, say about 20,
take an average of each of the first/second measurement
times. Each manufacturer of circuit breakers has published
values for what those readings should be (average.
The significant readings of circuit breaker testing are
not usually related to the timing of the contacts, yes the
contacts can cause a motor to briefly single phase for less
than maybe 2 complete power cycles but not enough to really
matter, the significant measurements are those of mico-ohm
or millivolt drop across the contacts and closing spring
tension.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / sam
i HAVE DONE THE TEST AND THE RESULTS ARE,( OPEN TIME-50,3ms
WHILE THE CLOSING TIME-72,2ms)
| Is This Answer Correct ? | 14 Yes | 8 No |
Answer / master
Closing time of the CB is 50 to 55 m.sec
Opening time is 35 to 40 m.sec
short opening time is minimizing the fault effect like arc
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / thayathidavan gopalan
Closing time is always greater than opening time.Closing a
breaker means you have to close against the inertia and it
is closing on no load normally.
Opening time should be fast as possible to interrupt the arc
fast to avoid damaging of the contact , It depends upon
the manufacture and design of driving mechanism ,make to
open as fast as possible.
opening during fault shall be as fast as good to maintain
system stability also
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / abhishek goyal
Whenever Loaded CB is interrupted during running time it
generate arc at CB contact area. If some fault happening
during running it will damage the electrical equipment so we
need to fast action to reduce damage or risk (for ex: Short
ckt and over voltage etc.).
At the closing time there is no current drawn by CB contact
So that, circuit breaker closing time is always higher then
tripping/opening time.
second reason of slow closing time for contact to reduce
damage or risk of contact tips or other parts (MAY be
manufacture point of view)
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / robert
when closing the breaker u are also charging the spring
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / btln
The circuit breaker closing time depends on the mechanisim
of the circuit breaker,normally the opening time should be
less to trip the breaker in short time to prevent the exess
arcing of the contats else it may damage the interrupter
during the arcing period.and for closing time the circuit
breaker mechanisim will take longer time to close the
breaker and it will be maintained with effective load with
contact loading springs to prevent pre arcing.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / krishnakumar
The circuit breaker is used for protection purpose and the main function is to trip(open its contacts) when relay gives the trip command.the tripping of breaker will isolate the healthy phase from faulty phase.if the tripping time is more t,then the fault will be present for more timing and this will damage the whole system.so the breaker should operate at high speed in order to protect the system.so,the tripping timing should be less.but in case of closing of breaker,there is no need as such as tripping at fault condition.and there is another phenomenon called bouncing that makes the timing increased than tripping time.if the timing is less for closing,then the breaker moving contact moves very fast towards the fixed contact and so the bouncing will be more due to the high speed.this is also a reason for more closing time
| Is This Answer Correct ? | 0 Yes | 0 No |
Iwould like to know barc interview questions
how to find the multiplication factor for digital energy meter and analog energy meter
What is stray looses?
A 1F capacitor is charged to 100V initially. A 1H inductor is connected accros the capacitor througha a switch. The current in the circiut when the switch is closed is____
What is minimum phase system?
how could we findout the lightning arrester failed or not in live circuit? Is there any instrument to measure the high voltage at the time of sky lighting?
Explain about how is it working Earth fault'relay and wahts the resistance value of earth bed
Sir, I need a power supply at 380V. The supply I get in three phase is rated 415V. The total supply I have from the supply company is 70KW. Kindly inform if it is better to use a voltage stabiliser for this purpose or a transformer
Comparision of Air break circuit breaker, SF6 Circuit breaker and vacuum circuit breaker.
what type of battery used for starting D.G?state its function?
how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula
WHAT IS THE DIFFERENCE BETWEEN NEUTRAL AND EARTHING
1 Answers Adani, Adani Power, Raychem RPG,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)