HOW TO FIND THE PRIMARY AND SECONDARY OF TRANSFORMER(IN OFF
CONDITION) USING MULTIMETER? IS IT POSSIBLE FIND BY SEEING
RESISTANCE???
Answers were Sorted based on User's Feedback
Answer / r.nandha kumar
yes,it is possible by measuring the winding resistance of
primary & secondary.High voltage side will have high
resistance value than th low voltage side
Is This Answer Correct ? | 36 Yes | 4 No |
as per working principle transformer , there is no primary &
secondary of transformer . transformer can be work in either
ways.
but if we have to check HV & LV we can do with multimeter .
as per transformer ratio
V1/V2=N1/N2=I2/I1. ................eqn 1
&
R =rho L/A . ...............eqn 2
\
as LV side requirement of current more & no of turns are
less , & cross sectional area of conductor is lare as per
eqn no.1& 2,resistance offered by conductor is less as
compare to HV .
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / desingurajan
initially transformer have no primary or secondary. wherever we giving input, that is called primary. and another end is called as secondary......
Is This Answer Correct ? | 23 Yes | 20 No |
Answer / rsbangra
As looking the tranformer one side primary and other side
secondary as per name plate, we can mesure resistenance by
just r=v/i v=rating voltage and i= rating current ,voltage
take root 3 of line voltage, so we recive resistanse value
ht or lt side, as other view insulatior are used ht side so
high and lt side lower leanth and small size.
Is This Answer Correct ? | 3 Yes | 3 No |
i have one source transformer with the capacity of 50KVA, connected with two loads 10kw and second one is 15kw.. how can i calculate first load in KVA and second one in KVA .. because Kva rating, power factor rating of of transformer is different from the load… there must be some way to calculate load KVA rating and power factor….
how will we calculate the copper wire load..
why transformer rating in KVA ?
8 Answers Bhel, TATA, Voltage,
How to create a SCADA diagram on PC? I run the DG everyday but i dont know how that animated single line diagram is created.Please answer.
1.After synchronising the alternator to the grid,how we r delivering power to the grid?if the i/p increases does the speed hence frequency increases? 2.y the power factor is changing when exitation changes?what is the relation with p.f and flux?
solar inverters was not connected to the nuteral link .this nutwral possible to any other systems
What is the function of the serge absorber?
explain how the power is distributed from a power plant to a consumer.explain step wise in detail
what is the range of thermal overload and over current. Answer should be in percentage of current.
Dear sir, we are getting voltage fluctuations suddenly for 2 or 3 minutes again it becomes normal. we checked each and every connection some times we are getting 110 volts like that from earth to neutral again it is reducing we are getting supply from 45 kva DG set give earthing properly.
Why Current Transformers cannot be connected in parallel
When semiconductor fuse does save thyristor in each cycle of conduction? Why under voltage setting keep less in SPRS and more in DC drive?