In 3 phase induction motor 1hp current rating is 1.5 amps
constant ? is correct or not ?
Answers were Sorted based on User's Feedback
Answer / jatin
the current rating of an induction motor depends upon the load . so the value of current will change as per the load and not remain constant at 1.5 amps
| Is This Answer Correct ? | 23 Yes | 6 No |
Answer / narendra korrapati
motor amps is depends upon load.if load increase on motor
the full load amps will be change.practicaly i saw a 3-
phase 1 hp motor takes 3.5 amps
| Is This Answer Correct ? | 13 Yes | 6 No |
Answer / m bilal akram
a motor have manufacture at limited load if we put on extra
load may b motor winding brake at full load motor take
constant current if voltage and power factor also constant
however its Change current also Change.if load change
current also change.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / pradyumna chandra panda
It is not justificable that current rating of 3ph motor is culculate to 1.5 amp per hp. Reactive power is more in higher size hp motor ie. slight less current per hp. And reactive power is less in lower size hp motor ie. more current per hp. Normaly 3ph 1hp motor take 1.8 amp per phase (phase current) Simiarily current rating of 3ph 5hp is 7.5 amp, 10hp is slight less then 15 amp and 100 hp motor is approximately 140 amp.
| Is This Answer Correct ? | 5 Yes | 2 No |
The unit of electrical charge is the
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT SWITCH BOARD,MLDB,ACB,BUSBAR,ETC...?
what is meant by 3rd hormonics ?
how to find insulation resistance of a motor(415v) by theoretical formula??
compare between starting charactristics of synchronous motor with those of 3Q Squirrel cage induction motor
what is the maximum permissible limit value of leakage current and leakage counter reading to replace lightining arrester?
Please send 110 kv sb station full single line drawing(sld)
what are the stresses in circuit breakers ?
how calculation to be done of cable size/o.h. conductor size of 11kv h.t.for the load of 2175 kw
What are the reason of unbalanced secondary voltage of HT transformer 33kv/6.6kv ? Incomming voltage is balanced.33kv each secondary voltage 6.6 kv 6.4 kv 6.4 kv At no load conditions.
What is difference between isolator and circuit breaker?
when we r using 3.5 cable for a bldg. and put laod on each phase using the neutral and neutral is the return paht for the phase so the current of the neutral must be Ir+Ib+iY (return).But the size of the netural is .5 as comper to the phase.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)