In 3 phase induction motor 1hp current rating is 1.5 amps
constant ? is correct or not ?
Answers were Sorted based on User's Feedback
Answer / jatin
the current rating of an induction motor depends upon the load . so the value of current will change as per the load and not remain constant at 1.5 amps
| Is This Answer Correct ? | 23 Yes | 6 No |
Answer / narendra korrapati
motor amps is depends upon load.if load increase on motor
the full load amps will be change.practicaly i saw a 3-
phase 1 hp motor takes 3.5 amps
| Is This Answer Correct ? | 13 Yes | 6 No |
Answer / m bilal akram
a motor have manufacture at limited load if we put on extra
load may b motor winding brake at full load motor take
constant current if voltage and power factor also constant
however its Change current also Change.if load change
current also change.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / pradyumna chandra panda
It is not justificable that current rating of 3ph motor is culculate to 1.5 amp per hp. Reactive power is more in higher size hp motor ie. slight less current per hp. And reactive power is less in lower size hp motor ie. more current per hp. Normaly 3ph 1hp motor take 1.8 amp per phase (phase current) Simiarily current rating of 3ph 5hp is 7.5 amp, 10hp is slight less then 15 amp and 100 hp motor is approximately 140 amp.
| Is This Answer Correct ? | 5 Yes | 2 No |
Define non-touching loop.
Ohm's law applicable for semi-conductors?
what is the difference between real and reactive power? and what is the importance of these
why the perameters of secondary circuit are more important then that of the primary circuit of induction motor?
Shall we get electrical shock if we touch the positive terminal of a 230 volt dc supply?
How to calculate & connection of 900KVA generator 2 sets & load(1500A)? How to choose cable size and ACB size for this load & generator? please explain me detail. Regards, Mr.Han
1.why we are using blocks in withoutgaplightning arrester 2.why we ar using bushing in withoutgap lightning arrestor
How i can calculate the cable size for given load,there is any formula,for 3 phase and single phase
2 Answers Prescient Technologies,
When do you use a VFD motor?
why effective resistance should be more than static resistance in transmission line?
how we select the fuse and OLR rating for 3 phase induction motor from 1HP TO 100 HP?
How to calculate the cable size in sq. mm. when the load is given in KW?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)