Explain the experiment on ward leonard method of speed
control of a dc shunt motor.
Answers were Sorted based on User's Feedback
Answer / vinodh kumar ks
A shunt motor speed is controlled by the field. Think of it
like this: The actual resistance of the armature is very
small so by Ohm's law the armature current (locked rotor)
will be very large. But as the motor turns it acts like a
generator and that generated voltage reduces the current
that the motor draws. Soon at no load the motor is turning
fast enough that very little current is required. if you
make the field stronger by increasing the field current the
generator action (called back EMF) is increased and the
motor doesn't have to turn as fast to balance the voltage
applied to the armature.
So the rule is reduce the field to increase the speed.
| Is This Answer Correct ? | 15 Yes | 7 No |
Answer / somasundaram t
ward leonard method is one of the dc motor speeed
control.this method requires combination of one motor
generator set for controlling the one DC motor.so this
method becomes expensive.and also requires high
maintanence.power consumption ,losses also more.this method
got too failure after the power semiconductor controllers
has been introduced.
| Is This Answer Correct ? | 6 Yes | 1 No |
model question paper for supervisor trainee
Which type of DG need Netral Earthing?
In a 11kv/433v transformer,at the LT side ie 433 V side why do we need to put 3.5 core Cable upto Panel.The full load rated Amps is 666 at LV side.What value of current will flow through the Nuetral Conductor.Why can't we use 4Core Cable instea of that?
we all know that corona is nothing but ionization of air around the conductor and there by allowing current to pass through ionized air.but we are not getting any short circuit in between the respective phases though the air turned as a conductive media between them??
Whag is the PS class of accuracy of CT?
What is the difference between Delta & Wye windings?
The capacity of the transformer is 20/25 MVA, Ratio is 132/11 KV, Vactor group YNyno. and impedance is 10.07%. As per the calculation the secondary current is 1312.2Amps. The maximum fault current the transformer should sustain is 13.030KA. How many times the transformer should sustain the maximum short circuit current of 13.030KA over a period up 1 Year. The transformer is repaired one & 10 Years old.
what is the difference between equipment earth and system earth.
In a flange coupling, the flange bolts are designed for
make control wire diagram of start and stop a function with a single push button
What does dny11 stand for?
what is relation of rpm with Power supply? rpm directly Proposational to power ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)