In a 11kv/433v transformer,at the LT side ie 433 V side why
do we need to put 3.5 core Cable upto Panel.The full load
rated Amps is 666 at LV side.What value of current will flow
through the Nuetral Conductor.Why can't we use 4Core Cable
instea of that?
Answers were Sorted based on User's Feedback
Answer / hanmanth reddy y
In a three phase system with star connected secondary
(433V side) if two phases are fully loaded to 666A and the
third phase not at all loaded the current through nuetral
conductor will be 666A. But in practice in a three phase
system that the third phase not having any load and other
two phases fully loaded is not in practice. If all the
three phases loaded equally no current flows through
nuetral and nuetral cable is not required.
Based on the requirment of transformer insulation nuetral
earthing has to be done at the transformer terminal only.
Nuetral is neccessary for single phase loads. If the
nuetral is dispensed entirely it is not possible to supply
power to single phase loads. Normally even in worst case as
huelistic judgement the nutral current will not exceed 50%
of phase current under unbalaced load conditions. Hence it
is appropriate to select cable of 3.5 core rather that of a
4 core cable.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / s.banik
we are always try to be distribute our load as balance
condition(i think transformer secondary side is star
connected),but in practical this not possible at
site.So,little current is flows through the neutral
conductor but this is not so high.some time we are use in
4core, this is depend on load condition & practical operation.
| Is This Answer Correct ? | 1 Yes | 0 No |
How does ELCB work when exist earth foult? and How does RCCB work when exist earth foult?
how can we Increase the Value Of Frequency in electric circuits
What does Bode plot tell you?
what is the difference b/w conductor and semicoductor
a new 3ph induction motor doesn't rotates their ratted speed, why ?
What is the meaning of EDO in DG panels?
As Electricity Generates in MW I w'd like to know What are the factors we have to consider regarding the transmission of electricity from generation station to Public uses(230 V)
if three phase supply is given to single phase transformer, what will happen?
Sir, plz tell me the relation b/w KW and frequency in Variable frequency Drive?
I have iti elec, 1st aid, and 5 yrs experience in 7.5 mw power plant. Am i eligeble for 11kv license in telangana state..when, how to apply for that.?
our scope called one core cable for distribution system so we like to use 4 core cable with one equipment grounding conductor so what kind of technical reasons i can say that the 4core is better then 1 core,
what is the RMU and RMU system in sub-station(11kv,66kv.....)
2 Answers Alstom, Torrent Power,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)