two transformers are separated by concreted wall becuase of
when any fault occurs which results in fire on any one of
transformer it protects the healthyone transformer.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / guru
If the distance between the transformers is more than the
requirement then firewall will not be required as per IER
1956 standards.
There is a minimum distance laid down in IEC1956 based on
the capacity, voltage rating of the transformers
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / tom hanks
Any two transformers in a plant/substation are always
seperated by a concrete wall known as BLAST WALL, (Blast
walls are generally 1000mm+ bigger the size of larger
transformer) It is protect the healthy transformer from
fire, incase the other one is on fire due to short-
circuit/oil leakage etc.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / shaji samuel
Two Transformers aside should be supperated by concreted
wall because through blast wall we prevent the two
transformers with each other fault,shortcircuit sparks, and
due to the blast of the oil tank of the transformer then we
can prevent the safe one transformer.
| Is This Answer Correct ? | 3 Yes | 0 No |
It is fire wall, during fault condition if transformer at
fire it should not spread to other equipment/buildings.
As per IS, the thickness should be 350mm brick wall/230mm
concrete wall. Height of the wall shall be decided based on
the height of x'frm
| Is This Answer Correct ? | 2 Yes | 0 No |
WHAT ARE THE DFT AND RMS MEASURMENTS PRINCIPLE IN NUMERICAL TECHNOLOGY OF POWER SYSTEM ?? WHICH IS BETTER IN WHICH QUANTITY MEASURNMENT??
what is the meaning of improving the power factor (give technical ans not therotical)
I have draw the 350A DC current, so what is the size of cable i can use? Give me the answer with formula
Can we use generator transformer as step down transformer? How?
What is the difference between the watt hour meter and Var hour meter in terms of internal connection and work theory . ie "When the meter records watt-hour an when the meter records var hours ??"
in india why we not use frequency above 50 hz for distrubuting power ?
WHAT IS AIR GAP VALUE IN MM FOR A 11KV BUSHING OF 11KV/440V DISTRIBUTION TRANSFORMER. AND AIR GAP VALUE OF 25 KV BUSHING OF AT TRANSFORMER OF 25 KV TRACTION. WHAT IS THE CALCULATION FOR THE AIR GAP PERMITTED FOR BUSHINGS AT DIFFERENT VOLTAGES.
how speed control of induction motor?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING) I O (current operating)?
what are upstream faults and downstream faults in power system
at which places we use 6.6KV Transformers and Motors
What is meant by operating sequence of VCB : 0–0.3sec.–CO– 3min.-CO
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)