we have taken HV test of 2.5 k and Megger test on 11 kv HT
cable.here it shows no fault but when we are charging the
same cable with 11 kv supply why the VCB 11 kv gets tripped
can anybody define the possible cause of fault ?
Answers were Sorted based on User's Feedback
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
| Is This Answer Correct ? | 1 Yes | 1 No |
Check out the control circuit. And every possible relevant thing in panel cable breaker.... Thoroughly.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
| Is This Answer Correct ? | 0 Yes | 1 No |
pls give me brif explaination about the distance relay.
what is the ciruit diagram of transformer vector grup test?
why DC source is used to idetify the polarity of CT/PT?
How we Use DC Power in Transformers? is it possible ?
If we have 11 kv RYB Phase single core cable near about. Then wht effect and losses
What is the Difference between Ac Drives and Dc Drives? According to application, speed, Torque, cost, Reliability, Construction, Motor etc... Thankyou !!!
sir please tel me how calucalte kwh if home taken load 30ams how maney kwh taken per day.and 3phase motor 5hp per hars how maney load teken and how mach kwh and forward me to electrical table for calicalte kwh and kvr and kvah
what is surge arresters ?........
Do we really need wheels for the transformer
how can findout cable fault Location only useing MEGGER
WHY IN AC DRIVES,INPUT PHASE CURRENT SHOW UNBALANCE?
what is mean impedance?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)