we have taken HV test of 2.5 k and Megger test on 11 kv HT
cable.here it shows no fault but when we are charging the
same cable with 11 kv supply why the VCB 11 kv gets tripped
can anybody define the possible cause of fault ?
Answers were Sorted based on User's Feedback
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
| Is This Answer Correct ? | 1 Yes | 1 No |
Check out the control circuit. And every possible relevant thing in panel cable breaker.... Thoroughly.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
| Is This Answer Correct ? | 0 Yes | 1 No |
why corona loss is less with negative polarity?
can we use 220 volt 15 w a.c. lamp on 220 volt d.c.
Natural frequency in the control system represents nature of a. Transient response b. Oscillations c. Overshoot d. Speed of responce
how can electricity is produced without water
when a primary current injection test is required, it is accomplished by what?
What is the difference between grounding & earthing?
how much cable size required for 70 kilowatt load.
Dear sir, How to calculate 3.5 core pvc aluminium armoured cable meter wise carrying amps rating.Please give the solution with a good example.
Why we are testing cables with dc?
There is 3phase power cable from 1 point to the other point which is 100m away. Two point equipped with power meter and recorded 1st point is 205kW while the 2nd is 202kW and each phase average carry 400amps. To calculate the resistance of the 3phase power cable, is the formula using will be P=I2R?
What will happen if power transformer designed for 50 Hz is connected to 500 Hz of the same voltage , and vice versa ?
in Contactor opearation Why there is a difference in the values of the operate and release voltage in case AC supply
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)