we have taken HV test of 2.5 k and Megger test on 11 kv HT
cable.here it shows no fault but when we are charging the
same cable with 11 kv supply why the VCB 11 kv gets tripped
can anybody define the possible cause of fault ?
Answers were Sorted based on User's Feedback
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
Is This Answer Correct ? | 1 Yes | 1 No |
Check out the control circuit. And every possible relevant thing in panel cable breaker.... Thoroughly.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
Is This Answer Correct ? | 0 Yes | 1 No |
Iam deepthi.i completed my b.tech from electrical engineering.i want to prepare for civil services.i dont have much knowledge about these exams,but i have great zeal of cracking exams.plz provide me suggestions to which options i can select for optionals
What would cause a 240v choke that should give 110v out on a 16w lamp to gradually increase to 160v?
In a single phase converter, the no. of SCR conducting during overlap? a.1 b.2 c. 3 d. 4
we have two generators different capacity on 15 MW and other 6MW at 11 KV , 15 MW gen. bus short level current 40KA,and 6MW short level current 25KA,, length of cable 100MTR between 6 MW from 15MW gen. for bus coupling . kindly tell any one can we use both NGR OR one NGR from any GEN. BOTH NGR has diff. rating. Tariq pakistan
what are the various parts of airconditioning system used in train and its working
What should be the conservator minimum oil level required in 2 mva transformer
What is Phase to Phase clearance for 800V System Operating Voltage as per IEC61439
why we use ac system in india why not dc
Why transformer rating is represent in KVA?
7 Answers Bhel, Sonalika, Usha Martin, Wipro,
if a 2 ohm resistor,2 ohm capacitor and a 2 ohm inductor is connected parallely to 12v source.Then what is the value of current in each branch.Is current flows in each branch at the same time?If not so then provide the proper sequence
What is the difference between generator and alternator?
why we use dc motor instead of ac motor?