Why the outpet og DG is 415V not 440V?
Answer / k.prakashchandra
Line voltage 440 V means phase voltage 250
v.,400-230,415-240.It depends on voltage rating of 1 phase
appliances used and also of three phase.Generally 230 V
class are used .Allowing for line drop, gen of 415 V line
voltage is preferred.
Is This Answer Correct ? | 2 Yes | 2 No |