What is basic fundamental for choosing NGR or NGT for any
generator neutral grounding
Answers were Sorted based on User's Feedback
Answer / vishal i vadodaria
As we know that in Y connection there are 3 phases [R,Y&B] & a neutral.
In neutral we provide a resistance & than we used to ground it.Such system called neutral ground resistance [NGR].
Why we use NGR?
AS we know ideally the sum of current Ir+Iy+Ib is zero. So in normal condition the current which flow through neutral of Y winding is very low.
In case of occurrence of phase to phase or phase to ground fault heavy unbalance current will be generated & that will flow through neutral. To restrict this current we provide a resistance in neutral.
If we do not provide resistance in neutral & fault occurs at that time a heavy current will flow & it cause excessive heating in stator winding & it may damage the winding. to prevent this we provided a resistance in neutral.
Is This Answer Correct ? | 60 Yes | 9 No |
Answer / vrishali ajagaonkar
CRITERIA-IN ORDER TO PROTECT THE STATOR CORE FROM DAMAGE
DURING INTERNAL EARTH FAULT IT IS NECESSARY TO LIMIT THE
STATOR EARTH FAULT CURRENT AL LOW AS POSSIBLE.MAY BE UPTO
10AMP FOR GENERATOR.
BASIS FOR SELECTION OF NGTR-
IF GENERATOR IS CONNECTED TO THE SYSTEM THROUGH GENERATOR
TRANSFORMER THEN GENERATOR CAN BE TREATED AS AN ISOLATED
SYSTEM WHICH IS NOT INFLUENCED BY THE DISTRIBUTION EARTHING
SYSTEM. IN THIS CASE YOU CAN SELECT EARTH FAULT CURRENT AS
LOW AS POSSIBLE, BUT IF WE USE NGR THEN IN ORDER TO LIMIT
THE LOW EARTH FAULT CURRENT SIZE OF THE NGR WILL BE
INCREASED.DUE TO BIG SIZE OF NGR WE REQUIRED MORE SPACE &
ALSO ITS TOO COSTLY.
V = IR MEANS IF V CONSTANT I IS INVERSELY PROPORTIONAL TO R
EXP:-TO LIMIT 10AMP CURRENT , V =11KV/ROOT 3
R = 11/ROOT 3/10*1000=635.10 OHM ( VERY HIGH VALUE)
FOR OVERCOME ON THIS, GENERAL PRACTICE TO USE A NGTR SO THAT
WE CAN LIMIT LOW EARTH CURRENT WITHOUT ANY EXTRA COST.
EXP:- NGTR 11/240V
TO LIMIT 10AMP CURRENT
CURRENT REFLECT ON SECONDARY SIDE OF NGTR WILL BE
= (11000/ROOT 3/240)*10=264.6 AMP.
RESISTOR VALUE ON SECONDARY SIDE R =240/264.6 =0.9 OHM (
APPROXIMATELY) WHICH IS MUCH LOWER THAN 635.10 OHM.
BASIS FOR SELECTION OF NGR-
IF GENERATOR IS DIRECTLY CONNECTED TO THE SYSTEM THEN WE CAN
NOT LIMIT THE EARTH FAULT CURRENT UP TO 10 AMP. WE HAVE TO
SELECT THE EARTH FAULT CURRENT VALUE ABOVE THE RESIDUAL
CAPACITIVE CHARGING CURRENT OF SYSTEM.ALSO WE NEED TO CHECK
THE POSSIBILITY OF RELAY SETTING OPERATION WITH CT RATIO.
FOR EXMP- IF CT RATIO IS 2000/1AMP & EARTH FAULT LIMIT
CURRENT IS 100AMP RELAY SELECTED WITH 10 % SETTING.
THEN THAT RELAY WILL SEE ONLY 200AMP EARTH FAULT CURRENT IT
WILL NOT OPERATE ON 100AMP CURRENT.
ALSO WE CAN NOT KEEP GENERATOR SOLIDLY GROUNDED BECAUSE OF
HIGH EARTH FAULT CURRENT STATOR CAN DAMAGE SAME WILL HAPPEN
WITH HT MOTOR IF IT IS CONNECTED TO THIS SYSTEM.
SO FOR THIS CASE WE NEED TO SELECT THE NGR WITH PROPER EARTH
FAULT CURRENT ( ABOVE THE RESIDUAL CAPACITIVE CHARGING
CURRENT OF SYSTEM) TO AVOID UNWANTED TRIPPING.
Is This Answer Correct ? | 43 Yes | 3 No |
why we are using panel space heaters in different control schemes????
During he starting up of the motor, the upstream's MCCB (350A) always trips due to the UVT relay activated. Can Star-delta starter use for a 20kW Motor (For a powder mixer machine) cause voltage-dip in the supply line voltage? If so, what are the recommended solution to eliminate/reduce the transient voltage dip in the line voltage?
I am getting diesel genset 62 kv for my house In addition there are 6 meters of 11kv for the house Lift also being installed for house plot sise 200sq yds total 4 + 2 foloors I want to know how much earthing required how deep it should be
For Electrical / and Electronic Systems, when we say efficiency is 80%, then what happens to other 20% from the Power consumption.? I.e. what happens to this?
Can a 50-Hz designed transformer be used at 60-Hz system? Is the same remains true, when a 60-Hz designed transformer be used at 50-Hz system? Consider only frequency variation. The voltage remains as rated value in all cases. Justify the answer.
what is the difference between star connected and delta connected motors
The speed of a dc motor can be controlled by the variation of 1. armature voltage. 2. field current. 3. armature circuit resistance. 4. angle of brush shift. Which of the statements given above are correct? (a) 1,2 and 3 (b) 2,3 and 4 (c) 1,3 and 4 (d) 1,2 and 4
I have an existing old MCCB. ABB Model SACE, the rating are: Ue = 660 volts, Iu =1250 Amps, 3 poles, Ith (max) =800 amps at 45 deg C. I need a circuit breaker for my 3 phase motors, 380 volts 60 hz. the supplier required the minimum ampacity of the breaker to be 911 amps. can i use this breaker with rating of Iu =1250 amps but Ith = 800amps maximum?
what do you mean by switchgears?
5 Answers Practical Viva Questions,
1.generator rated as 1000 mva,11kv .8 pf what will 0.8 pf will indicate? 1.max pf it can supply 2.min pf it can supply like this 4 options there what is answer.explain
what sort of general awareness questions are asked in o.n.g.c entrance exam?????????????????
why DC source is used to idetify the polarity of CT/PT?