Answer / vishal i vadodaria
As we know that in Y connection there are 3 phases [R,Y&B] & a neutral.
In neutral we provide a resistance & than we used to ground it.Such system called neutral ground resistance [NGR].
Why we use NGR?
AS we know ideally the sum of current Ir+Iy+Ib is zero. So in normal condition the current which flow through neutral of Y winding is very low.
In case of occurrence of phase to phase or phase to ground fault heavy unbalance current will be generated & that will flow through neutral. To restrict this current we provide a resistance in neutral.
If we do not provide resistance in neutral & fault occurs at that time a heavy current will flow & it cause excessive heating in stator winding & it may damage the winding. to prevent this we provided a resistance in neutral.
Is This Answer Correct ? | 60 Yes | 9 No |
Answer / vrishali ajagaonkar
CRITERIA-IN ORDER TO PROTECT THE STATOR CORE FROM DAMAGE
DURING INTERNAL EARTH FAULT IT IS NECESSARY TO LIMIT THE
STATOR EARTH FAULT CURRENT AL LOW AS POSSIBLE.MAY BE UPTO
10AMP FOR GENERATOR.
BASIS FOR SELECTION OF NGTR-
IF GENERATOR IS CONNECTED TO THE SYSTEM THROUGH GENERATOR
TRANSFORMER THEN GENERATOR CAN BE TREATED AS AN ISOLATED
SYSTEM WHICH IS NOT INFLUENCED BY THE DISTRIBUTION EARTHING
SYSTEM. IN THIS CASE YOU CAN SELECT EARTH FAULT CURRENT AS
LOW AS POSSIBLE, BUT IF WE USE NGR THEN IN ORDER TO LIMIT
THE LOW EARTH FAULT CURRENT SIZE OF THE NGR WILL BE
INCREASED.DUE TO BIG SIZE OF NGR WE REQUIRED MORE SPACE &
ALSO ITS TOO COSTLY.
V = IR MEANS IF V CONSTANT I IS INVERSELY PROPORTIONAL TO R
EXP:-TO LIMIT 10AMP CURRENT , V =11KV/ROOT 3
R = 11/ROOT 3/10*1000=635.10 OHM ( VERY HIGH VALUE)
FOR OVERCOME ON THIS, GENERAL PRACTICE TO USE A NGTR SO THAT
WE CAN LIMIT LOW EARTH CURRENT WITHOUT ANY EXTRA COST.
EXP:- NGTR 11/240V
TO LIMIT 10AMP CURRENT
CURRENT REFLECT ON SECONDARY SIDE OF NGTR WILL BE
= (11000/ROOT 3/240)*10=264.6 AMP.
RESISTOR VALUE ON SECONDARY SIDE R =240/264.6 =0.9 OHM (
APPROXIMATELY) WHICH IS MUCH LOWER THAN 635.10 OHM.
BASIS FOR SELECTION OF NGR-
IF GENERATOR IS DIRECTLY CONNECTED TO THE SYSTEM THEN WE CAN
NOT LIMIT THE EARTH FAULT CURRENT UP TO 10 AMP. WE HAVE TO
SELECT THE EARTH FAULT CURRENT VALUE ABOVE THE RESIDUAL
CAPACITIVE CHARGING CURRENT OF SYSTEM.ALSO WE NEED TO CHECK
THE POSSIBILITY OF RELAY SETTING OPERATION WITH CT RATIO.
FOR EXMP- IF CT RATIO IS 2000/1AMP & EARTH FAULT LIMIT
CURRENT IS 100AMP RELAY SELECTED WITH 10 % SETTING.
THEN THAT RELAY WILL SEE ONLY 200AMP EARTH FAULT CURRENT IT
WILL NOT OPERATE ON 100AMP CURRENT.
ALSO WE CAN NOT KEEP GENERATOR SOLIDLY GROUNDED BECAUSE OF
HIGH EARTH FAULT CURRENT STATOR CAN DAMAGE SAME WILL HAPPEN
WITH HT MOTOR IF IT IS CONNECTED TO THIS SYSTEM.
SO FOR THIS CASE WE NEED TO SELECT THE NGR WITH PROPER EARTH
FAULT CURRENT ( ABOVE THE RESIDUAL CAPACITIVE CHARGING
CURRENT OF SYSTEM) TO AVOID UNWANTED TRIPPING.
Is This Answer Correct ? | 43 Yes | 3 No |
hai iam arunkumar. i have applied for an section enginner in rrb. i want lat 5 years solved question papers. if u have please sedn it to arun30682@gmail.com
What is the use of Surge Capacitor in LAVT?
how to check IR values in alternator winding?
What is the technical reason for adopting color coding of three phase system as RYB.
What are the voltage values for LT,HT,EHT and other voltages??
hi this toufik here. i am doing my b.e.degree.now i am in final year and supposed to do a project in this year so i thinking to control the buchholz relay using software base means checking the status of transformer oil using microcontroler, plc or scada. so can i do so...??? alz suggest me...
what are the maximum available current, voltage ratings and switching speeds of the power electronic devices thyristor, power mosfet, igbt, and mct?
In scott connected transformer number of turns in the primary winding of teaser transformer is % of number of primary turns of main transformer A 86.6 B 57.7 C 14.4 D 33.3
respected sir, sir recentely i have applied for chennai and tiruvananthapur section enggineer and juniour engg in electrical dept. but still i donot get how i have to syart my preparation and also t the same time i donot know exactly what they r going to give in the examinations i mean which sections they r going to give i donot know exactly, can u prefer whichh books i have to follow and model papers or both boards
how to calculate current when LT supply 415v fed to HT Motor 6.6kv and 1120kw.
What is the basis for selecting Vk/2 or Vk/4 for REF and Differential protection of Transformer and What is the significance of magnetising current
How does a VOLTAGE OPERATED DIFFERENTIAL RELAY work??