why neutral and body earthing of transformers kept
separated? what is distance between two is required as per
is?
Answers were Sorted based on User's Feedback
Answer / pramod sawant
1.Body earthing is used for body leakage current to earth &
not human body harmful.
2. Neutral earthing is used for
unbalance current pass through neutral & its goes to earth
& not effect on other phases voltages/load.
Is This Answer Correct ? | 32 Yes | 3 No |
Answer / ashish jani
body earthing used for transformer leakage current to avoid
human injury and use for transformer protection.
Neutral earthing used for transformer unbalance current of
transformer.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / vimal
It's not neutral earthing.its called neutral grounding. Like NGR NTR
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / brijesh
Body earthing is ued for earth the leakage current passing
through equipment body. the other purpose is to protect
human body against passing the leakage current.
Neytral earthing is used for giving an earth path to
unbalanced current. It also ballance the voltage in each
phase.
Is This Answer Correct ? | 2 Yes | 1 No |
if not separated,suppose neutral is not working
properly,then in case of lightning on the body of
tranformer then very large current will flow through body
earthing wire to neutral earthing wire.So it will be
dangerous for transformer.
so to avoid from destruction both body earthing & neutral
earthing are separatly properly earthed.
Is This Answer Correct ? | 5 Yes | 4 No |
Answer / engr.shahbul
Body earthing is used for body leakage current to earth without
human body harmful.Neutral earthing is used for giving an earth path to
unbalanced current. It also balance the voltage in each
phase.suppose neutral is not working
properly,then in case of lightning on the body of
transformer then very large current will flow through body
earthing wire to neutral earthing wire.So it will be
dangerous for transformer.
so to avoid from destruction both body earthing & neutral
earthing are separately properly earthed.Minimum 3meter
Is This Answer Correct ? | 1 Yes | 0 No |
sir please send me iocl written test paper in my e-mail account. i'll be obliged to you........ thank u roshan
How to calculate cable size in sq units based on motor rating is KW
how to calculate ups and battery rating
In HI POT test what is reason for applying the AC VOLTS and DC VOLTS in different applications what is the nessesity for this ?
why cont we short earth and N.......?
what is differnce between oil transformer & dry type transformer ???????????
which one is rotating transformer-single phase induction motor or 3 phase squirrel cage motor?
When alarm is activated in buccholz relay in transformer
When the relative speed between the magnetic fields of stator and rotor does is zero under steady state operation?
what is the size of trasmission conducatar
Alternating voltage and current is which type of quantities?
We have 800KW motor operating at 6600Volt,50 Hz supply.During 1st startup it tripped on overcurrent trip.It's FLA is 88 Amps.The K factor of Thermal overloaaad was set on .94 initially.then we set at 0.97 and then it started fine.i dont understand why it tripped first?What are the protections which comes in picture during starting ?