The wire is disconnected from the temperature sending unit
(magnetic gauge). A voltmeter connected to the wire reads
0v. What does this indicate?
Answers were Sorted based on User's Feedback
Answer / nikhil patil
While transmitting the signal the concept of active and
live zero is used.Generally 1V to 5V is standerd signal
range.voltmeter will read 1v when input to the system is
minimum (active zero)and voltmeter will read 0V when wire
is disconnected.Hence troubleshouting becomes easy.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / ravi gandhi
As per my thought ,
1 > Sensor is there in feild , that will give Temp reading
in Volt / Resistance that will fetch by TT (Temp
Transmitter)when the wire is disconnected & Volt meter is
showing 0 Volts that means two leads of wire may be
shorted .Even o\p of TT is 4-20 mA Voltmeter reading will O
Volts inplace of 1-5 Volts .
TS --- >> TT ----- > Voltmeter(Connected perellel)
| Is This Answer Correct ? | 1 Yes | 1 No |
How is SmartPlant Instrumentation related to INtools?
i want the equation of this question. Tranmitter range is 120 mmwc and dcs flow range is 1700 nm3/hr. if i want to change dcs range from 1700 to 2400 nm3/hr then how much dp i have to enter in transmitter
i hav applied for the post of engg. in iocl so please require the past test papers fro instrumentation engg please please help me and send me the papers or tell me the pattern and type of ques asked in examination......
where uses EXe /EXd/Exo/Exn/Exp/Exq/EXia
capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of known density so if you wanna callibrate it just close block valve just before capilary @ high side & connect druck apply it's calibrated range pressure as normal calibration ensure low side block valve must be closed & if you asking commissioning so this is not a DP type pressure tx so simple if you wanna put in servie this tx just open high side block valve & than low side block same way i do it but still transmitter showing -13 ma.just tell me what i want to do ?
Coriolis flow meter coil supply is 24vdc but why still we given 230ac for this transmitter let me explained detailed review please
How to calibrate a temperature transmitter & how a Cold junction Compensation will be carried out?
When a timer is placed in RS Logix 5000 with preset value less than its scan time it is malfunctioning. i.e., if the preset is set to 30ms still the timer TT bit is counting till 150ms(its scan time). Any solution for the problem?
1. How can leveltrol be installed in steam drum for measuring the level of steam drum?
Explain " FAIL SAFE " feature in temp. measurement.
1 Answers Bapco Bahrain Petroleum Company,
PT RTD Range: -200 to 500 degree celsius If I configured in DCS Lower range and Upper range . In face plate it shows red colour due to overa range how was the characteristics look If the temperature is more than operating range. how was the characteristics look . whether its in Resistance vs Temperature curve is Linear or Non linear
i want all model questions paper for robert bosch
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)