how can we measure the pressure in underground cooling
water pipeline by using pressure transmitter?what about the
tapping position?
Answers were Sorted based on User's Feedback
You can install the PT anywhere on the pipe. It is best to
install on top in crude and slurry application but to
measure water you can install any where, even under the pipe.
If you install on the side or under the pipe fill the
impulse line with water then do a zero on the PT before you
do the final span calibration. Also remember that the
calibration you do on the PT must be exactly the same as to
what your DCS or SCADA faceplate have been scaled to. In
other words if you calibrate the PT for 0 to 20Bar you must
make sure the faceplate in the CCR are also scaled to 0 to
20bar.
Good luck
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / carl_ellis
If the transmitter is not directly mounted on the
underground pipe, which is not unusual unless there is
vault access, then an impulse tube/pipe has to come up out
of the ground. The pressure measurement will be in error,
low, by the difference in elevation between the pipe's
elevation and the pressure transmitter's elevation.
Suppose the pipe is 2.1m below the grade level and the
pressure transmitter is 1.6m above grade. The elevation
difference is 3.7m.
The measurement is 3.7m or 0.362 bar low.
It is not unusual to have water supplied at pressure
between at 4-8 bar. At 4 bar pressure, an error of 0.36m
water column is a 9% error, a vary large value for an
insturment capable of 0.25% or better accuracy.
The commissioning of the unit should include the
appropriate zero correction to compensate for such a large
error.
Carl Ellis, Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
How to Calibrate Level Switch in field
What is pressure,What is temperature,What is flow,What is level
WHAT IS THE DIFFERENCE BETWEEN PLC AND DCS
55 Answers ABB, Adani, Adani Power, GMR, IIUC,
Im having problems with interfase betwen SPI v7.0 and SPPID v5.05. Previous versions of Intools shoul be fixed with SPPIDproj.ocx file. It was necessary to replace this file with one that allows the connection between different versions of SPPID. It is necessary in the current version to do the same?Thanks
What is loop1 and loop2 in MTS LT?
How to convert mA into Percentage?
How to measure the vibration..?
Make a ladder diagram on LSL valve will close, on PSL valve will open and start the motor
What are advantages and disadvantage of the ac supply load cell?
Name different types of bourdon tubes.
how flame detectors sense the flame.
what is proportional & what is proportional band
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)