how can we measure the pressure in underground cooling
water pipeline by using pressure transmitter?what about the
tapping position?
Answers were Sorted based on User's Feedback
You can install the PT anywhere on the pipe. It is best to
install on top in crude and slurry application but to
measure water you can install any where, even under the pipe.
If you install on the side or under the pipe fill the
impulse line with water then do a zero on the PT before you
do the final span calibration. Also remember that the
calibration you do on the PT must be exactly the same as to
what your DCS or SCADA faceplate have been scaled to. In
other words if you calibrate the PT for 0 to 20Bar you must
make sure the faceplate in the CCR are also scaled to 0 to
20bar.
Good luck
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / carl_ellis
If the transmitter is not directly mounted on the
underground pipe, which is not unusual unless there is
vault access, then an impulse tube/pipe has to come up out
of the ground. The pressure measurement will be in error,
low, by the difference in elevation between the pipe's
elevation and the pressure transmitter's elevation.
Suppose the pipe is 2.1m below the grade level and the
pressure transmitter is 1.6m above grade. The elevation
difference is 3.7m.
The measurement is 3.7m or 0.362 bar low.
It is not unusual to have water supplied at pressure
between at 4-8 bar. At 4 bar pressure, an error of 0.36m
water column is a 9% error, a vary large value for an
insturment capable of 0.25% or better accuracy.
The commissioning of the unit should include the
appropriate zero correction to compensate for such a large
error.
Carl Ellis, Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
there is one orifice plate already installed on 3" line, but my previous engineer(who is not working here) removed that tx, but now i want to take it in to the process, so now what i have to do now? flow fluid is hytherm oil of temp. 260deg & pressure is 3bar.
What pressure transmitter.
I need the intools training institute address in india. Intools subject oriented local authors books.Refer me plz
In RS 500 SLC 5/03 input change one module card to another card, plz. give steps clearly.
plz you help about Que paper of mahagenco previous your,any model paper relad to it{maharastra power genration}
䑰ҕ䔈ҕ䖠ҕ䘰ҕ䛀ҕ䝐ҕ䟐ҕ䢐ҕ䥐ҕŹ
whey we conect ammeter in series and voltmeter in parallel in circuit
Can we use a 10000 Lph Flow Transmitter in 100 LPH flow line to get 20mA O/P by adjusting SPAN ?
where using the 0-20ma in feiled instrumentation? why its using?
what is difference between HART communication and BRAIN communication?
Dear sir i m presently working in power plant nd my question is if any pump give flow 18tph then how would i know that how much range flow tx installed their flow line for flow measurement plz give me ans
what is wave length were using ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)