if power factor comes in leading & showing -0.95. Is there
any effect on electrical system? if yes, then please tell me
what would be the effects. & how long we keep power factor
in leading.
Keeping power factor in leading shows more KW & less KVA is
it correct or not.
Answers were Sorted based on User's Feedback
Answer / santosh kawade
It is not recommended to keep power factor leading:
1) We try to keep power factor unit to reduce transmission
losses, this main purpose will not achieved by keeping
leading power factor. If power factor is lower than unit
(it can be leading or lagging) transmission loss will
increase.
2) During leading power factor if we make any breaker
operation (close/open)it will generate high voltage across
breaker, which is harmful to breaker. For capacitive load
operation we need a special breaker.
3) It is not correct that keeping leading power factor
shows more KW and less KVA.
Santosh Kawade
9224 69 3116
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rahamadulla.m
Yes there is effect on electrical system.The power will be
lost and could not maintain the voltage in the capacitor
bank system. so we can keeping power factor in leading
shows more KW and less KVA.It is correct.
| Is This Answer Correct ? | 2 Yes | 2 No |
how to calculate efficiency of voltage and current controlled welding transformer?
Can any body tell me what is use of END OF LINE RESISTOR in fire alaram circuit?
magnetic circuit consume energy
The basis on which voltage selection of motor is done i.e. either HT or LT.
what is the use of providing earthing for tanks? i know for lightning we use earthing ? Here one of my ONGC project there is no need of lightning protection and there is no power connection near by tank in that situation also ONGC asking earthing for tanks but we didn't understanding why they asking earthing? is anybody tell exact answer?
Essential condition for parallel operation of two single phase transformer is that they should have same A polarity B kVA rating C voltage ratio D % impedance
how do u calculate CT rating for 10 mva transformer
how to find out this one mcb r mccb?
What are the application of filter?
75kw drive operated motor current fluctuation from(85-130)ampere.current setting in drive is 130amp.sometimes motor trip when current limit cross 130amps.I change the drive. still current fluctuate between 80-130amps but in this time motor not trip,current setting in drive is 130amps.where is the problem?
What is the instrument to check the rotating diode fuse of alternator in running conditions?
In our plant we are having 6.6 v motor wih MV drive running frm last two years.udenly at some speed motor getting vey vibrations what is the problem
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)