if power factor comes in leading & showing -0.95. Is there
any effect on electrical system? if yes, then please tell me
what would be the effects. & how long we keep power factor
in leading.
Keeping power factor in leading shows more KW & less KVA is
it correct or not.
Answers were Sorted based on User's Feedback
Answer / santosh kawade
It is not recommended to keep power factor leading:
1) We try to keep power factor unit to reduce transmission
losses, this main purpose will not achieved by keeping
leading power factor. If power factor is lower than unit
(it can be leading or lagging) transmission loss will
increase.
2) During leading power factor if we make any breaker
operation (close/open)it will generate high voltage across
breaker, which is harmful to breaker. For capacitive load
operation we need a special breaker.
3) It is not correct that keeping leading power factor
shows more KW and less KVA.
Santosh Kawade
9224 69 3116
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rahamadulla.m
Yes there is effect on electrical system.The power will be
lost and could not maintain the voltage in the capacitor
bank system. so we can keeping power factor in leading
shows more KW and less KVA.It is correct.
| Is This Answer Correct ? | 2 Yes | 2 No |
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is observed the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
If a capacitor bank is having rating 750kvar for 6.6kv. Then for 3.3kv how much will be the rating of capacitor bank.
give me atleast four differences between circuit and network
As you achieve greater success with the company after some years, Will you like to be a share holder in our company?
How does a transformer contribute towards the widespread popularity of ac system over dc?
In a company the lines carrying 33KV but the load is below 10000Volts so we know that <11KV we can put 11KV lines but the lines are 33KV,..so how we can step down the voltage to 11KV with out erecting a substation
basic princple of induction and synchronous motor
WHAT IS THE COMPLETE DEFINATION OF POWER FACTOR?HOW IT CAN BE IMPROVED?AND WHAT IS CAPACITIVE LOD AND INDUCTIVE LOADS
How can we check ELCB trip current sensitivity How can we check earth resistance value
Our Alternator nameplate specifies a power factor of 0.8. When the Alternator is on light load, the bus bar voltage rises to 11240 volts, whereas the standard value is 10500 volts. Is it ok to increase the power factor to 0.85 or 0.9. I am afraid because the power factor on the name plate is only 0.8 ?
1.dg on load alarm/stop alarm... 2.dg on load. piu alarm alarm kaise chek krte hai
what is meant by loss of field in a DC motor? how a universal motor works?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)