if power factor comes in leading & showing -0.95. Is there
any effect on electrical system? if yes, then please tell me
what would be the effects. & how long we keep power factor
in leading.
Keeping power factor in leading shows more KW & less KVA is
it correct or not.
Answers were Sorted based on User's Feedback
Answer / santosh kawade
It is not recommended to keep power factor leading:
1) We try to keep power factor unit to reduce transmission
losses, this main purpose will not achieved by keeping
leading power factor. If power factor is lower than unit
(it can be leading or lagging) transmission loss will
increase.
2) During leading power factor if we make any breaker
operation (close/open)it will generate high voltage across
breaker, which is harmful to breaker. For capacitive load
operation we need a special breaker.
3) It is not correct that keeping leading power factor
shows more KW and less KVA.
Santosh Kawade
9224 69 3116
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rahamadulla.m
Yes there is effect on electrical system.The power will be
lost and could not maintain the voltage in the capacitor
bank system. so we can keeping power factor in leading
shows more KW and less KVA.It is correct.
| Is This Answer Correct ? | 2 Yes | 2 No |
HOW TO FIND THE PRIMARY AND SECONDARY OF TRANSFORMER(IN OFF CONDITION) USING MULTIMETER? IS IT POSSIBLE FIND BY SEEING RESISTANCE???
What is the capacity of the Fastners 12mm?
A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.
How can we select suitable capacity generator for three phase load (inductive load) and how to take study analysis in 3 three phase load system ?
if 20 hp motor starts directly stars and contenious run . what will be the effect.
11 Answers HP, Ohsung Electronics,
what is the main parts of transformer? how it is functioning? pls giv the ans briefly.
why distribution transformer are of DY11 type?
How generator NPS(NEGATIVE PHASE SEQUENCE TEST)TEST WAS DONE? PROCEDURE WITH DETAILS?
What happen if the 24 volt DC supply is disconnected from air circuit breake ?
Can a 5 core cable one end with a 32A 3p+N+E plug and the other end 32A 3p+E be used on a generator?
a distribution transformer(3 phase)supplying 440volt per phase.now suppose one of phase voltage(230volt) becomes zero.what will be the cause ?
What are the circuit models used for analysis of medium length transmission lines? Which one is superior? Support your answer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)