Essential condition for parallel operation of two single
phase transformer is that they should have same
A polarity B kVA rating
C voltage ratio D % impedance
Answer / cyril
A, C and D.
Polarities of the two transformers must be the same. Otherwise, emf inducted in the 2 secondaries in parallel will cause a flow of circulating current through them, even without a connected load.
Voltage ratios must be the same. Otherwise, there will also be a flow of circulating current in the 2 secondaries if there is a voltage ratio difference.
Percentage impedance must be the same since load sharing of the transformers in parallel depends on the percentage impedance of the transformers.
Is This Answer Correct ? | 11 Yes | 3 No |
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage. note--it is tested with 5000 kv megger and insulation resistance is 0.05 M ohm. and some time 0.03 M ohm comes.
What should be the Sandwitch type Al. bus bar capacity for 2 M.W.Gen. set, having continuous full load current- 3463 Amps,ambient temp.- 50 Deg. C., Required temp. raise-20 deg.C., it will run 24 hrs, 365 days on full load, required highly reliable.
Write a note on RC operational amplifier as integrator
HOW TO CUT A CAKE IN 8 PIECES IN 1 STROKE
why dc supply is given to the field of alternator
why impudance relay used for medium transmission power system? why not others?
I have current, kva How can calculate kv?
WHY BREAKER ARE USED IN SUBSTATIONS?
what is a relay?
how much power consumed by 1.5 ton capacity split A.C in 1 hour
how to reduce earth to neutral voltage?
what is the difference between potential transformer and capacitive voltage transformer?