Answer / dinakaran
Normally neutral is connected to the earth.In that neutral
line we are connecting ct bcoz of sensing the earth fault to
protect the transformer winding against earth fault.
Is This Answer Correct ? | 33 Yes | 2 No |
Answer / vinod
Neutral CT is connecting between the neutral of transformer
and earth.(neutral bush of T/F to CT P1, CT P2 to earth).
This CT (PS Class) out put is using for REF (Restricted
earth fault protection of transformer winding)ie.REF is
operate only winding earth fault
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / md ekram
Normally neutral is connected to the earth.In that neutral
line we are connecting ct bcoz of sensing the earth fault to
protect the transformer winding against earth fault.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / amal raj
neutral is connected to the earth.In that neutral
line is connecting ct for sensing the earth fault to
protect the transformer winding against earth fault.
Is This Answer Correct ? | 2 Yes | 0 No |
What is the normal phase difference between the voltage and the no-load current in a transformer?
How generating electric power export to grid from the generating station ?
ell me capacitor bank chossen formula.load in KW
wt wil happen if a 120kv line is grounded
How to choose primany and secondary side MCB
why white color LED light is not possible?
We in my plant one of the transformer showing neutral to earth voltage is 22V how to solve it
how many load we can take for lighting
a simple c++ program to calculate simple interst with its data members as private
Why we use 4-20 mA Analog signal for the PLC input? Why not 0-20 mA? Why not 5-25 mA?
In three phase supply why we use R Y B Colour not other.
what is the difference between line voltage meter and relays