what is meant by neutral Ct of a transformer and how it
connected in transformer
Answers were Sorted based on User's Feedback
Answer / dinakaran
Normally neutral is connected to the earth.In that neutral
line we are connecting ct bcoz of sensing the earth fault to
protect the transformer winding against earth fault.
| Is This Answer Correct ? | 33 Yes | 2 No |
Answer / vinod
Neutral CT is connecting between the neutral of transformer
and earth.(neutral bush of T/F to CT P1, CT P2 to earth).
This CT (PS Class) out put is using for REF (Restricted
earth fault protection of transformer winding)ie.REF is
operate only winding earth fault
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / md ekram
Normally neutral is connected to the earth.In that neutral
line we are connecting ct bcoz of sensing the earth fault to
protect the transformer winding against earth fault.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / amal raj
neutral is connected to the earth.In that neutral
line is connecting ct for sensing the earth fault to
protect the transformer winding against earth fault.
| Is This Answer Correct ? | 2 Yes | 0 No |
as we see that in our country the power rating for transmission is always rated in multiple of 11 like 11kv,33kv,66kv132kv. So i want to know wht is reason or logic here.
what is sevice settings for mccb?How can be it setted?
how to calculate the KVAr for an motor for improving the PF
What do you mean by cold shinkable cable joint.How it is done.
I want to know the principle of rotating flux transformer.
Why the colour of insulator is always is chocolate in colour?
what is a bus riser in power system and why it is used
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
what is a breaker fail relay
What are m circles?
In a single phase converter, the no. of SCR conducting during overlap? a.1 b.2 c. 3 d. 4
Any one can explaination about calibration with rotating sub standards?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)