Answer / iamdon
The CT secondary should not be left opened secondary due to
following reasons:
1)Zero current in secondary leads zero back emf.So primary
current becomes very high.Large heat generated may burn the
winding and core.If the transformer sustain this heat, even
then its operation becomes improper as explained below.
2)CT is bascially a step up transformer.So high voltage
induced in secondary may saturate the core (core becomes
permanently damaged).So the operating point advances in non
linear region,which makes the transformer operation improper
(secomdary current will not replicate the primary according
to the turn ratio).
3)High voltage induced in secondary side may endanger the
life of personnel working on the side.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 16 Yes | 2 No |
Answer / bhautik patel
due to the absence of the counter ampere-turns of the secondary, the unopposed primary mmf will set up high flux in the core which will produce excessive core loss with subsequent heating & high voltage across the secondary terminals.
| Is This Answer Correct ? | 3 Yes | 0 No |
sir, my question is that if we start any three phase induction motor with star connection.will be current taken ? please send a formula.
How much voltage we need to apply in 33kv cable during hipot test of cable
What are the significant parts of dc generator?
What is 11 N1 and 12 N2 in single phase Transformer ?
what is a lightning arrester???
In which reason, one end of CT secondry get connected with Earthed? Normaly S1 of CT. Why????
in a diesel generator is there any relation between AVR to fule system?
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?
Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example?
If I want to use capacitor banks at HT (11 KV) side for maintaining power factor then which type of capacitor should I use? Plz give me the specification?? (I am using 1250 Kva transformer (11 KV/433V)).
If an electrical component has a positive temperature coefficient, how come such components have high power losses due to heat if current decreases when resistance increases? assuming power given by I^2*R whereby the Resistance is infinite.
why generation of electricity in low value voltage
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)