IF i have switchgear with busbar current rating of 1000Amp
35kA then is it necessary to have outgoing breaker kA rating
to be equal to busbar kA rating?
Answers were Sorted based on User's Feedback
Answer / rajender mohan
The Busbar Rating specifies the maximum short circuit current it can see and operate, so you can put a breaker up to breaking capacity of busbar,
Ambience temprature has to taken into consideration while designing the LT Panel.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / opselvaraj
Not neceesary but it is preferable to have the same rating
from operation/maintenance point of view.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / anil jangra
KA rating of any switchgear is depending on fault level of connecting load,so it necessary to calculate the fault current of load than select the switchgear rating,as per my opinion the must be able to clear the fault without damaging it self and healty one feeder also.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pravin deshbhratar
yes, whatever fault current rating that we are maintaining
for the Incomer breaker same has to be maintained for
outgoing breaker also unless there is a stepdown
transformer in line. Because the fault level is calculated
on the basis of actual load of the substation that it is
going to carry out, so it is suggested that we have to use
the same KA ratiing for Incomer as well as the Outgoing
breaker.
| Is This Answer Correct ? | 1 Yes | 4 No |
Not Necessary,depend upon your system means you are going
to use same KA rating for reactive power or normal power.if
you are using for reactive power then you hava to have same
KA rating of BB.however, you can check for normal load.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / r.gunasekaran
Circuit breaker KA rating should be more than that bus bar
KA.
| Is This Answer Correct ? | 0 Yes | 4 No |
what is the calculation of power factor?
what is advantage in open delta connection?
In a house wiring why we are using only one neutral wire and so many phase wires from the main board, when the load is common for both wires?
What is the difference between cylindrical-type and sandwich-type winding?
How can I calculate the fault level of a transformer. 1. If fault is 3phase fault 2. If fault is 1phase fault 3. If fault is 2phase fault Dear all geniouses, can you help me by giving answer. If anybody want to send something then mail me at "msalam_shahin@yahoo.com"
What is advantages of ungrounded neutral?
why vaccum circuit breakers are preferred over m.o.c.b
Why do we pefer VCB over OCB?What are the advantages of VCB over OCB?
different between grounding & earthing?
how to calculate the no load current in transformer?
what is meant by impedance & transient protection?
What is a system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)