what is cogging in motors?
Answer / iamdon
Cogging phenomenon is seen in the case of 3 phase Induction
Motor(SCIM-Squirrel Cage Induction Motor).
When number of stator and rotor slots are exactly equal and
polarity of conductors facing each other in slots is
opposite,In such cases, there is a magnetic locking between
facing conductors housed in stator and rotor slots.Since
the rotor inertia is large so motor does not start at
all.This is called Cogging.
This is avioded by skewing the rotor conductor slots over
the surface by angle in the range of 5 degree.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 33 Yes | 1 No |
What is difference between Earthing, Ground and Neutral?
1 Answers ABB, ABC, Indo Asian,
What are thermo couple cables and where they are used.
FOR 16/20 MVA 132/33 KV ONAN/ONAF TYPE TRANSFORMER IT IS DESIGNED FOR 16 MVA WITH ONAN CONDITION.IT BECOMES 20 MVA UNDER ONAF CONDITION.LOAD LOSS IS GUARANTEED FOR 65KW AT 20 MVA AND % IMPEDANCE 13.75. PLEASE TELL US AT WHAT LOAD LOSS AND % IMPEDANCE IT SHOULD BE DESIGNED FOR 16 MVA AND WHAT WILL BE ITS EFFICIENCY AT 20 MVA?
what are the settings is there for ABB REM543 Generator Protection Relay
What is BKW of Motor. And what its significance
WHAT IS THE USE OF TERTIARY WINDING IN A STAR/DELTA TRANSFORMER ?
How to connect a Restricted earth fault relay for 2000KVA,11/0.433 KV Distribution Transformer and What is the neutral CT ratio should be selelcted for 2000 MVA Transformer for estabilishing the Restricted earth fault relay
pls give me brif explaination about the distance relay.
How to select the different contactors ( starter combination) for different AC motors? what about fuse cappacity 4 different motors too?
In my 3 phase 4 wire electrical system N to earth voltage is 0.08 is it ok What is standard for it ?
If there are two transformer having rating of 2.5mva, 6.6kv/440v(satr-star),and the load is 600kw then what is better to maintain less losses in transformer having both transformer in parellel or only single transformer connected to load? Please give calculated answer
why we permissive overreach in distance protection.where it is applicable to use in long r short lines
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)