We operate a 10 Mw facility and we have been experiencing
several trips due to fluctuations on the MVAR? We have
checked all issues related to the AVR and we have found all
OK? Can anyone help us? The grid voltage, internal voltage,
all regular parameters look ok. MVAR fluctuate and there it
goes the unit? What could be happening? Thanks!
Answers were Sorted based on User's Feedback
Answer / chaitanya
this may happen due to the variation of reactance produced
by the capacitors connected to that line/....isolate one by
one under observation...and this can be sorted out on
timely basis,,,,
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / raj
I agree with chaitanya this may happen due to the variation
of reactance produced
by the capacitors connected to that line it will be better
to maintain the Power Factor 0.90 only every where and the
next and only cause is that AVR problem may be some loose
connection in power as well as control side because AVR has
to take care of that MVAR.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / naresh
this could be because of the interturn winding losses that
takes place in the lines.this factor may increase the MVAR
rating of the system,which infuence the performance of thea
system.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / manish
Generator AVR have got two setting either to fix MVAR or
according to load if u set them to fix MWAR generation
probably it will solve ur problem to a extent also look at
load pattern first.its really helpfull when you have synch
operation with grid.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.j.pailwan
Please check CT connections, CT Specifications and
saturation of particularly B phase as this CT feed back is
used in AVR during PF control mode while pareller with grid.
Is This Answer Correct ? | 0 Yes | 0 No |
what is meaning of 230volts ac 50hzs ac supply is it rms or maximum to getting ac 230v what amount of max voltage they will send
what is mppt (maximum power point tracking ) and how they used in solar power generation ??? what are the main components used in mppt?????
what is meant by flywheel and its role in retardation test
Why we are using Ohm's law? where it is applicable? explain.
10 Answers Pyramid Saimira, TCS,
HOW TO SIZE THE TRANSFORMER OR WHAT ARE THE STEPS INVOLVED IN FINDING THE SIZE OF THE TRANSFORMER FOR GIVEN LOAD SAY 2000KW ?
what gas is present in incandescent and florescent bulbs
Do u know any one? how to find out in motor rated amps? formula?
Metal covered multiconductor cables shall employ a marker tape located within the cable running for its complete length in lieu of cable surface marking. Is it true or false?
Why synchronous motor is used in power factor improvement,dc series in lift
why secondary terminal of current transformer should not be open circuited?
EXPLAIN WORKING PRINCIPLE OF ALTERNATOR & MOTORS.
What is slip in an induction motor?