what is ceiling voltage in an exciter?
Answer / raghavendran
Consider a Generator operating in three different conditions
when operating at rated load,the AVR applies rated DC
excitation to the field.But consider a condition when there
is a sudden load throw off, the terminal voltage at the
stator will be increased.To compensate for the sudden
increase in voltage level, the DC Exc is reduced
drastically.This is called as 'Negative Ceiling Voltage'.
But when there is a sudden increase in load the terminal
stator voltage drops due to external reaction effect.Hence
the drop in terminal voltage is compensated by sudden
increase in DC Exc.This is called as 'Positive Ceiling
Voltage'.For this the response time of the AVR has to be quick.
The minimum and maximum ceiling voltages may range upto 1.5
times the DC Exc voltage at No-Load and Full Load respectively.
| Is This Answer Correct ? | 48 Yes | 4 No |
what is the defination of Cable database? What are the points are considered while preparing cable database? Is there any sample available for cable database?
what is diffrent of RCCB & MCCB
Safety devices in SF6 Circuit Breaker?
While connecting the flood light plug on to the 415 V distribution panel,there was spark and the cable got burnt. Three ignitors of the flood light also burnt of. The lamps are of 400 W (total 6 lamps) connected through 1.5 mm2 cable. The plug was immediately removed from the circuit. There was a 30 mA RCD connected and a 250 A MCCB; however both did not trip. What could be the possible reasons for the circuit devices not to trip?Can someone assist please. Additional info if needed can be provided.
What's the differs between voltage & current & emf.
what is maximum or Threshold value of current 7 voltage that a common man can withstand
What is the working principle of CFL & T5 tube light & 40W tube light with electronic ballast?
Why the efficiency of generator is more than motor in swinburne's test
What is a captive power plant?
why we use core type and shell type transformers?
how we select the mva rating of the circuit breakers?
dear friends, we are use 130 hp load run with 0.98 power factor ( 38KVAR capacitor connected ). if we need improve the the power factor to 1 (unity). how much kvar capacitor to be add. have any formula? please share with me.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)