Answer / gunasekaran
insulation properties of SF6 is 2-3 time than air and it is
electro negative gas so it absorb more electron at the time
of fault and normal operating condition.in acb current
chopping is occur it is will make arc between the breaker if
you go high voltage.in vcb vacuum is good insulator than air.
so higher voltage level we r using vcb SF6 breaker
Is This Answer Correct ? | 24 Yes | 6 No |
Answer / mohammed amjath
In high voltage we use SF6 or VCB.Because if we go to ACB
the arc quenching will no be proper.Where as if we use vacum
or sulphur hexafloride the arc quenching will be 100percent.
Is This Answer Correct ? | 19 Yes | 6 No |
Answer / x man
DURING SWITCHING THEY PRODUCE HIGH ARC,SO BY USING VACUM
AND SF6 THE ARC CAN BE EFFECTIVELY QUENCHED.
iF ACB can be used every were they why do we need at the
other protective devices.so every thing has purpose for the
invention.
Is This Answer Correct ? | 23 Yes | 14 No |
Answer / baskaran.r
in an acb the distance between terminals are fixed for 415
volts. for higher voltages this need to be much larger.
there are some makes acbs are available in 3.3 kv with
increased gap to the tune of 2 feet. For higher voltages the
gap required will be very much higher.arc handling will be
impossible in higher voltages
Is This Answer Correct ? | 17 Yes | 10 No |
Answer / deepak kumar
because in acb time required to extinguish the arc is much
more as compare to sf6 & vcb,if we use acb at higher
voltage , very large amount of heat will produced during
abnormal condition( short ckt) that will damage the acb or
complete circuit
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / kuldeep mehla
Beacuse Dielectric strength of vacuum & SF6 gas is more as compared to ACB. Therefore, for maintaining dielectric strenght to quench the arc at the same voltage level the size of ACB will be more compared to VCB & SF6. Therefore, ACB used in low tension line mostly.
Is This Answer Correct ? | 2 Yes | 0 No |
According BIS,IEC standards in HT lines the Isc that current
is very highly making arc that arc is quenched by the SF6 or
vcb. If ACB has used the breaker contacts & cables are burn
out at Isc.so we used SF6 & vcb has used in HT lines for
safety purpose
Is This Answer Correct ? | 2 Yes | 6 No |
why most of junction box vendors providing T5/T6 Temp class jb's for T3 area any special reason?
what is the illumination level required for child play area?
when a machine act as genartor and as motor?
which level of transformer oil has got low dielectric strength ?why?
For an induction motor wat is the loading/unloading cycle duration or interms of L/UL ratio/ percentage?
difference b/w semiconductor and dielectric
why a tester wont shock while testing the power in house
What is the Designing & Selection Procedure for a DG/Transormer of rated capacity?
How to design the no. of ceiling fans required in 5mtr X 10 mtr X 3 Mtr hight room?
IF we want to replace I/C bay at our 220 kv substation which is of 140 mw load capacity bay to be replaced by 400 mw capacity bay.other than CT(1200/1) what are the other equipment i have to replace.
A thermistor is a type of
How to Calculate The sag of OPGW in Transmission Line???