How to decide the input and output circuit breaker for a
1600kva transformer.Is there any calculation is involved.
Answers were Sorted based on User's Feedback
Answer / basayya
1600kva transformer
p= root3*v*i*cospai 1600kva*1000=1600000
1600000/1.732*400*1=2309.46
total current= 2309.46
u can use transformer sec side acb 2500A
i think
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / rajeshsan
The circuit breaker is selected based on following factors.
1. Voltage level
2. Fault current.
3. Type of Breaker.
4. Operating Time.
5. Number of operations.
| Is This Answer Correct ? | 1 Yes | 0 No |
it depends on the condition where transformer is put into
the service in the power systems because impedence vary
with these so fault current also varies
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / lokesh ranjith
Depend upon the contract demand the transformer will be
nstalled for full load ex: input will 850AVCB
output will be 2500A
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / baskaran.r
the high voltage side the rating will be according to fault
level of the system and primary current. the secondary
rating also according to the full load current of the
transformer
| Is This Answer Correct ? | 2 Yes | 3 No |
how was your last weekend.
How can we get electric power from lighting ?
when a airgap of the induction motor gets larger does it draw more current ??? does it power factor gets lower?
While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply
what is the difference between phase and neutral?
3 Answers IAF, Indian Airlines,
WHAT IS MEANT BY SLIP , WHERE IT OCCUR
what are problems caused by the pdu in rack server
Why neutral cable carry current.
what is difference between fuse and breaker?
role of europe union in UK safety legistlation (electrical safety)
Why star pointed terminal have no current? how?
what will be the energy loss =? Voltage drop = ? Conductor resistance at 20 degree C = ? Temprature convertion Factor at 50 degree c = ? on ACSR DOG Condutor at following data. distance = 4.8 kM Load = 2980 kWh Size of Conductor = 6/ 0.186 Volt = 11 kV.
1 Answers Pakistan Atomic Energy Commission PAEC,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)