How to decide the input and output circuit breaker for a
1600kva transformer.Is there any calculation is involved.
Answers were Sorted based on User's Feedback
Answer / basayya
1600kva transformer
p= root3*v*i*cospai 1600kva*1000=1600000
1600000/1.732*400*1=2309.46
total current= 2309.46
u can use transformer sec side acb 2500A
i think
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / rajeshsan
The circuit breaker is selected based on following factors.
1. Voltage level
2. Fault current.
3. Type of Breaker.
4. Operating Time.
5. Number of operations.
| Is This Answer Correct ? | 1 Yes | 0 No |
it depends on the condition where transformer is put into
the service in the power systems because impedence vary
with these so fault current also varies
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / lokesh ranjith
Depend upon the contract demand the transformer will be
nstalled for full load ex: input will 850AVCB
output will be 2500A
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / baskaran.r
the high voltage side the rating will be according to fault
level of the system and primary current. the secondary
rating also according to the full load current of the
transformer
| Is This Answer Correct ? | 2 Yes | 3 No |
which gas is cost wise high?
What is Star Delta Connection, where it is applied & what for it is used
4 Answers Premium Transmission,
ouestion for the post of section engineer
how to measure earth pit resistance
7 Answers BARC, BYD Electronic, Construction,
The readings with a Multi meter are 15 Amps Phase Neutral 192,Phase Earth 194 and Neutral Earth 24 5 Amps Phase neutral 192, Phase Earth 153, neutral Earth 48
How to calculate the transmission losses incase of overhead transmission lines?
what is MUSS?
funtion of choke
we have provided 30 nos. relay contacts in panel.I want to know how do we do the numbering for the relay contacts as per any applicable standards
how to calculate circuit breaker capacity
why permanent magnet generator have higher frequency of 400hz
what will happen at the time of CT saturation?and what will be the Relay's function at the time of CT saturation?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)