why transformer rating is expressed in kva.
Answers were Sorted based on User's Feedback
Answer / nitiniitp
kVA is the unit for apparent power. Apparent power consists
of active and reactive power. Active power is the share of
the apparent power which transmits energy from the source
(generator) to the user. Reactive power is the share of the
apparent power which represents a useless oscillation of
energy from the source to the user and back again. It
occurs when on account of some »inertia« in the system
there is a phase shift between voltage and current. This
means that the current does not change polarity synchronous
with the voltage. But the heat generated in a winding as
well as the eddy current losses generated in a transformer
core depend on the current only, regardless of whether it
aligns with the voltage or not. Therefore the heat is
always proportional to the square of the current amplitude,
irrespective of the phase angle (the shift between voltage
and current). So a transformer has to be rated (and
selected) by apparent power.
| Is This Answer Correct ? | 26 Yes | 0 No |
Answer / rahul faye
there are 2 types of losses in transformer are core loss and ohmic loss...as these losses depend on voltage and current. and are almost unaffected by the load pf.. that's why transformer rating is expressed in kva nt in kw....
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / lokeshraj
For t/f rating kva is used because at the time of
manufacturing of t/f we dont know about the value of the
cos(angle).As Power(KW)=kva*cos(angle).....
....Lokesh
| Is This Answer Correct ? | 6 Yes | 12 No |
Answer / mrithun
The power factor of transformer is unity.
Since KW=KVA*cos(phi)
KW=KVA*1 (in case of transformer)
KW=KVA
So transformer is rated in KVA and not in KW.
| Is This Answer Correct ? | 3 Yes | 11 No |
What is the difference between AVR and Servo Stabliser
what is bus pt and what is the function of it
i want to know how to calculate the battery capacity based on the UPS . ex i want to run have one kva UPS Which should run 10 hours ? in that case how many batteries to be installed and what will be the AH Value .
What will be the impact on motor performance if a LT motor is rewound with changed motor winding data as given below:- Original winding data: total 04 wires = 02 wires of 17 SWG + 02 wires of 16.5 SWG. Changed Winding data: total 03 wires of 15.5 SWG wire size Motor rating: 160KW, 740RPM, 415V, ID FAN application. Normal Running Current = 95% of FL Current.
Safety of dry type transformer
what is busbar. how many types of starter.what appartus will be used to improve voltage.what is the function of starter.what is b.h.p.what material is used for earthing.
Leading power factor means what? what is the power factor value while in power factor is leading? is power factor greater than one? In some cases i heard pf 0.8 leading then what about 0.8 lagging?
1 Answers Rockfort Engineering,
explain different losses in a transformer.
Why electrical engineer use Cu Strip for transformer neutral why not GI Strip? What if we use GI instead of Cu does it affects the transformer performance.
what is the circutor?why we use it ?
Earth leakage relay basic knowledge principle
how will protect transformer agint overcurrent protection
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)