what is an rmu?its circuit diagram.functions
Answers were Sorted based on User's Feedback
Answer / sivakumar
RING MAIN UNIT IS A 11 KV OR 33 KV HT PANEL HAVING 3
BREAKERS THAT IS 2 FOR INCOMING ONE FOR OUT GOING. IT
ENABLES CONSUMER USE 2 SOURCES OF HT POWER IN A THE SAME
METERING POINT i. e RMU.
| Is This Answer Correct ? | 135 Yes | 32 No |
Answer / santosh
If there are two nos of ht power we have used to ring main
unit panel. In case of power failer from one source we can
take power from another source at the same point.
| Is This Answer Correct ? | 104 Yes | 12 No |
Answer / khalid mahmood
RMU IS A DISTRIBUTION SUBSTATION.IT PROVIDES MEDIUM VOLTAGE
POWER SUPPLY 11KV 13.8KV 22KV 33KVS.TWO CIRCUITS PROVIDED
FOR FEEDIND ALTERNATIVELY & ONE FOR TO FEED THE TRANSFORMER
EQUIPED WITH OVER CURRENT AS WELL AS EARTH FAULT PROTECTION
RELAYS TO PROTECT THE TRANSFORMER.I HIGHLY RECMEND THAT TWO
FEEDERS SHOULD BE INTERLOCKED TO AVOID THE OPERATION
SIMELTANEOUSLY.
| Is This Answer Correct ? | 50 Yes | 7 No |
Answer / zafir alam
Ring Main Unit used in high voltage Distribution
System.There's flexibility in the supply in this system.
| Is This Answer Correct ? | 52 Yes | 21 No |
Answer / dixit
RMU is a panel generally forms ring system in which distributor is supplied from more than 1 feeders as input to RMU so that in case of failure from any one feeder ,power can be fed uninterruptedly from another feeders at the same point.
Now a days it is of SF6 gas insulated type.
| Is This Answer Correct ? | 33 Yes | 8 No |
Answer / ramandeep
used for two input of ht and one out put for ht ..
used for given the supply at same time .when one supply
will be fail ....& most important is we have to provide
interlocking between two incomer so that at a time only one
incomer can be ON . other it may short circuit
| Is This Answer Correct ? | 29 Yes | 8 No |
Answer / santosh bansal
Ring Main Unit
used for two input of ht and one out put for ht ..
or same one input and two out put ....
used for given the supply at same time .when one supply
will be fail ....
| Is This Answer Correct ? | 27 Yes | 16 No |
Answer / khalid mahmood janjua
RING MAIN UNIT IS TO BE USED TWO INCOMMING AND ONE OUT GOING GENERALLY BUT SOME TIMES ONE INCOMMING AND TWO OUT GOINGS MEDIUM VOLTAGE SUPPLIES.IN ENGINEERING DISTRIBUTION THIS IS CALLED FLEXIBLE POWER SUPPLY.NO A DAY SF6 CIRCUIT BREAKERS GOING TO BE USED.THESE ARE MAINTENANCE FREE BREAKERS.REMEMBER THAT SOLID WITH EPOXY RESIN CAST ALSO USED THOSE ARE NOT LATEST BUT ARE COMPATIBLE TO INTERNAL STANDARDS.
| Is This Answer Correct ? | 16 Yes | 5 No |
Answer / jitendra patil
what is interlock in rmu (sf6breaker) bitween two or three isolator?
| Is This Answer Correct ? | 5 Yes | 1 No |
How to calculat size of copper & aluminium ?
In winding design, the angle of chording (β) is nearly equal to A 45 degree B 60 degree C 30 degree D 90 degree
How to calculate or testing the KW in generator
how do i convert 22kw to kva
how much current take 16sq mm Cable
what is vA rating and class of a ct.
why are u join ntpc
why the vfd motor take current high in vfd panel then mcc panel.current in vfd panel=160A in 93%.and mcc panel it shows 130A. (132kw motor)
please write motor, transformer, Generator setting, fault level calculation of Tr.etc
If current and resistance in a circuit is increased by 20%, what will happen to its voltage drop??
is it value of power factor is more than unit. whats effects in the source supply
any one guide me to reduce the power factor of diesel Generator from 0.97 Leg to 0.8 Leg.with out any change in my load.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)