how much current take 16sq mm Cable
Answers were Sorted based on User's Feedback
Answer / hari
in 16 sq mm cable aluminium air 64amps ground 71amps duct
60amps temp 35degrs
in 16 sq mm cable copper air 83amps ground 92amps duct
72amps temp 35degrs
Is This Answer Correct ? | 19 Yes | 2 No |
Answer / karan
You can refer to the cable manufacturers details and most
of them are availale on the net.
Is This Answer Correct ? | 2 Yes | 4 No |
What are series and parallel isolators?
What percentage netural current is in netural depend upon the phase current
Why is it not possible to operate a star-delta transformer in parallel with delta-delta transformer?
why magnetising curve not start with zero voltage?
What is Magnetic Current Test of Transformer.
ceiling fan wattages rating
plz send me the procedure and syllabus for mseb exam
if the supply voltage increased by N times, the x-section of conductor will be.........
2 Answers APGenco, Electrical Tech, Ericsson, IES, Thirumalai Chemicals,
if a single phase 3 hp submersible pump of Crompton Greaves is moving in reverse direction and sometimes it moves in rigth direction ,then what may be the cause....
What is the difference between voltages or potential difference? And what are they?
( Re: WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR CAPACITOR BANK Answer # 1 The capacitor current would be kvar x 1000 / (415 x sqrt3). This would be 70a approx. The MCCB selected should have *atleast 1.4 times this current i.e. 1.4 x 70= 98. So you should choose at least 100 A mccb.) regarding to this answer,i would like to know why the current have to times 1.4 to get the right amphere for the mccb.hows the formula to get the 1.4??tq
what is the voltage level which is used in transformer short circuit test