why the vfd motor take current high in vfd panel then mcc
panel.current in vfd panel=160A in 93%.and mcc panel it
shows 130A. (132kw motor)
Answer / prasanna kumar
motor running with star-delta starter or DOL will show full
load of the motor unless the motor drawing high currents due
to faults.while coming to the vfd motor may run at high
speed or low speed acc to the requirement.when it was
running with high speed it will draw more current.
| Is This Answer Correct ? | 1 Yes | 1 No |
How to convert KVA rating into HP rating?
Explain Energy and Power signals?
why the admittance matrix or y bus matrix of a large network is called sparse matrix?
if There is Short circuit in Power Transformer, what will happened to Buchholz Relay.?? How Buchholz Relay will respond.??
What would be the size of wire used for 2 Ton of window A.C?
PAC and simple Ac different
The potential difference between a phase and neutral is 230v , but the potential difference between two phases is 400v. why?
if earthing is used in place of neutral how the circuit completd.
how air lock will be removed from generators, how it happens?
why ac generator ratings in kva only why not kw ????????????? ?
how to calculate the megger values for motors and cables?
tell me working of air circuit braker.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)