why the vfd motor take current high in vfd panel then mcc
panel.current in vfd panel=160A in 93%.and mcc panel it
shows 130A. (132kw motor)
Answer / prasanna kumar
motor running with star-delta starter or DOL will show full
load of the motor unless the motor drawing high currents due
to faults.while coming to the vfd motor may run at high
speed or low speed acc to the requirement.when it was
running with high speed it will draw more current.
| Is This Answer Correct ? | 1 Yes | 1 No |
what is mean by harmonics
If a contactor need to replace with faulty one. what I want to check?
why voltage between neutral and earth, with out secondary grounded distribution transformer
Why ideally the internal resistance of voltmeter should be infinite and of an ammeter be zero
When a 25kV line touches the train, will passenger get shock?
1)why the transformer rating in KVA insted of KW 2)why the secondary of ct is shorted and why the PT secondary is open
from where the self excitrd induction generator get the power?why is the voltage regulation is poor of seig?
what is the difference between the electrical and electronic choke?
why batteries are rated in ampere hour
in transmission line 11kv is step up or step down? why?
Describe: Energy efficient motors
what is saturation in transformer
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)