what is reactive power and active power
Answers were Sorted based on User's Feedback
Answer / ullas k prabhu
Answer interms of the formula...
active power= V*I*cos(angle bw voltage and current)
reactive power= V*I*sin(angle bw voltage and current)
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / laxminarayana
The powe which is in phase with current is called active
power and which is perpendicular to the current is called
reactive power
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / denzel101
Reactive power is the power consumed by highly inductive
loads like induction motors (windings are highly inductive)
and supplied by capacitors
(power factor correction). in some cases this power can be
supplied into a power system by means of condensor motors
which can be made to run at leading or lagging power factor
depending on thier excitation.
Active power is mainly consumed by pure resistive loads
like a bulb or an electric kettle.
In a pure inductive load, the power factor is lagging
because the current wave lags behind the voltage wave by 90
degree.
In a pure capacitive load, the power factor is leading
because the current wave leads the voltage wave by 90
degrees.
A pure resistive loads has no phase shift. The current and
the voltage waves reaches maximum and minimum values at the
same time.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / toshi
ans:Reactive power is defined as the swinging
power,swinging between the source and the load. it is
actually used for energising the reactive elements.
whereas, active power is defined as the consumable power or
it is the lost power.
it can also be defined as the power dissipated in the
ressitive circuits.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the differance between transformer neutral solidly earthed and transformer neutral earthed through resistor?
i have a 4 Mva transformer 34.5 kv / 480-277 v and i used 2 parallel 3200 amp bus duct for the secondary feeder using 3 ply of bus bar ( 3/8" x 5" ) as a common where the flexible link terminated and 6300 amps breaker for the main, the lower bus duct reaches 70 degrees and the upper bus duct reaches 55 degrees when i used thermal scanner. why the temperature is not balance when the load reaches 3600 amps.
sir what is the minimun earth resistance value of an industial bit and grid bit ? and Why?
For 6600/433 distribution transformer we apply secondary side 433 volts how much voltage in primary side.
transformer is working or not with supply of DC?
explain the meaning of harmonic resonance
in 4 pole lap wound dc motor one brush is disconnected then what result in new voltage if its voltage is v volts power is p watts current is i amp
why field winding is placed on rotor winding not on stator winding in case of synchronous machine?
why transformer rating in kva and motor rating in kw
we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440v?
10rm cable can got load ---- amp? Or Which Size Cable can take the load 100amp capacity SCR; breaker.
1 Answers B-Con Trade Associates,
in india are trains run by DC or AC? if DC , from where it receives negative potential? because pentograph receives singe potential only?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)