how to match 0 -10V with 4 - 20mA
Answers were Sorted based on User's Feedback
by using "transuducer" we can convert any electrical signal
into 0-10v and 4-20mA
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / dubai
As said by praveen, i would like to add one point to this
answer.
0-10 volt is an analog value which is first converted to
digital value via A/D convertor in PLC analog input module
& then D/A conversion is done by converting to 4-20 mA.This
is known as analog scaling.
Transducers are used as analog input device.They have zero
& span setting which scales the value as :
0 V=4 mA
10 V=20 mA
| Is This Answer Correct ? | 3 Yes | 0 No |
how would you come to know if a transformer is double wound or auto? note that there is no tag. you are given only a multimeter.
what is the thumb rule or formula for cable size and current ratings
Single line diagrams for star to delta and DOL starters.
transformer is connected with 50hz and 60hz at same rating which will give more output on same rating
what is power factor in ac ckt ?
What is DC series motor?
What is the effect of electric motor stuck in star configuration,
A rotor of an induction machine is delta connected. Now is there any necessacity to short the slip rings?
Wy transformer ratings are in multiple of 11 always?
what is power load and lighiting load?
Define the three phase formula fuse.
how to identify the cable quality and what is flame proof cable
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)