HT motors are generally connected in star, what will be the
effect if we connect HT motor in Delta?
Answers were Sorted based on User's Feedback
Answer / iamdon
star coonection reduces the voltage appering across each
phase by root 3 times.It means we need to design the
insulation for lower voltage which is economical.Also due
to reduced voltage reduced currrent will flow through
winding so less loss so less heating of winding so less
cooling requirement for keep the temperature rise within
limit.
All these beauty will lost in delta connection.So delta is
not preferred..
Is This Answer Correct ? | 42 Yes | 3 No |
Answer / nishad
If we are connecting the HT motor in Star, the starting &
load current will be decrease 57% as compaire to Delta
connection.
In the cause of our HT motor (11KV - 780 FLA, 14MW)drawing
arround 4250 A at the time of starting. It's just equal to
6 times of full load current. as per manufactore, it's
locked rotor current is 4280A. so just think, what will
happened if that connected in Delta!!!!!
Is This Answer Correct ? | 14 Yes | 5 No |
Answer / social worker
if u don't knew the answer just mind your buisness
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sivaraman
Why not we connect HT Motor in Delta also.i am working like
this type of motors only. But starting current has 6 times
of the full load current for our motors. it may decrease
and increase as per IS ( depending on the Capacity also ).
Is This Answer Correct ? | 7 Yes | 6 No |
Answer / girja shanker
If we connect HT motor in Delta connection then the voltage
in winding will equal to line voltage.
Is This Answer Correct ? | 6 Yes | 20 No |
I think the H.T. motor is connected in star, to take its
grounding point.
Is This Answer Correct ? | 3 Yes | 17 No |
what is the difference between fc-tcr and tsc in facts
3 Answers SCET Shadan College Of Engineering and Technology,
what will happen if i connect or change line with phase terminal
Will MCB tripped off, if there is an electric shock to Human body?
How to design the NGR Resistance
what happenes if two voltage source connected in parallel will be connected to load.
considering the 3phase and single phase ac system the load applied and the volage given is same...will the current differs for both the cases are it wil remain same?
how to put cable sizing and cable glands size for respective cable & Cable Lug size in a DB sectors???
Why power genaration in India is at 50HZ while America its 60HZ
How can i check a relay good or not?
compressor compresses air means exactly what happens?
difine electrical ballast in HPSVL
what is the difference between 5P20 class CT , PS Class CT and 5P10 class CT??