HT motors are generally connected in star, what will be the
effect if we connect HT motor in Delta?
Answers were Sorted based on User's Feedback
Answer / iamdon
star coonection reduces the voltage appering across each
phase by root 3 times.It means we need to design the
insulation for lower voltage which is economical.Also due
to reduced voltage reduced currrent will flow through
winding so less loss so less heating of winding so less
cooling requirement for keep the temperature rise within
limit.
All these beauty will lost in delta connection.So delta is
not preferred..
| Is This Answer Correct ? | 42 Yes | 3 No |
Answer / nishad
If we are connecting the HT motor in Star, the starting &
load current will be decrease 57% as compaire to Delta
connection.
In the cause of our HT motor (11KV - 780 FLA, 14MW)drawing
arround 4250 A at the time of starting. It's just equal to
6 times of full load current. as per manufactore, it's
locked rotor current is 4280A. so just think, what will
happened if that connected in Delta!!!!!
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / social worker
if u don't knew the answer just mind your buisness
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sivaraman
Why not we connect HT Motor in Delta also.i am working like
this type of motors only. But starting current has 6 times
of the full load current for our motors. it may decrease
and increase as per IS ( depending on the Capacity also ).
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / girja shanker
If we connect HT motor in Delta connection then the voltage
in winding will equal to line voltage.
| Is This Answer Correct ? | 6 Yes | 20 No |
I think the H.T. motor is connected in star, to take its
grounding point.
| Is This Answer Correct ? | 3 Yes | 17 No |
Why transformer is rated in kva?
CPC cable .PVC \1C....I want to get sure that type is flexible indoor or to be install on trench. please advice .thanx :)
What is a single phase autotransformer?
critically criticize the application of ring main unit in power system
Why we use a H.T. Fuse from a thick wire, on other side we use high rating of cables? & Why we use less Sq. mm Cable on H.T. side , on other side we use Large Sq. mm cable?
various transmission tower like .,D tower ,K.C.O tower ,C.C.O tower,K.C.R tower ,C.C.R tower ,H.C.O tower in different tons.
What is rotor angle stability?
how capacitor buield up the voltage
what is the applicatyons of the slipring motor and please tel me more about the slipring concept
what r the safety measures in UPS ? explain all?
What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.
why the efficiency of generator is more than the motor in case of swinburne's test????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)