HT motors are generally connected in star, what will be the
effect if we connect HT motor in Delta?
Answers were Sorted based on User's Feedback
Answer / iamdon
star coonection reduces the voltage appering across each
phase by root 3 times.It means we need to design the
insulation for lower voltage which is economical.Also due
to reduced voltage reduced currrent will flow through
winding so less loss so less heating of winding so less
cooling requirement for keep the temperature rise within
limit.
All these beauty will lost in delta connection.So delta is
not preferred..
| Is This Answer Correct ? | 42 Yes | 3 No |
Answer / nishad
If we are connecting the HT motor in Star, the starting &
load current will be decrease 57% as compaire to Delta
connection.
In the cause of our HT motor (11KV - 780 FLA, 14MW)drawing
arround 4250 A at the time of starting. It's just equal to
6 times of full load current. as per manufactore, it's
locked rotor current is 4280A. so just think, what will
happened if that connected in Delta!!!!!
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / social worker
if u don't knew the answer just mind your buisness
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sivaraman
Why not we connect HT Motor in Delta also.i am working like
this type of motors only. But starting current has 6 times
of the full load current for our motors. it may decrease
and increase as per IS ( depending on the Capacity also ).
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / girja shanker
If we connect HT motor in Delta connection then the voltage
in winding will equal to line voltage.
| Is This Answer Correct ? | 6 Yes | 20 No |
I think the H.T. motor is connected in star, to take its
grounding point.
| Is This Answer Correct ? | 3 Yes | 17 No |
What is required of exietation to the alternater.
WHATS THE DIFFERENCE IN USING THE 125% AND THE 250% FACTOR OF SAFETY IN CALCULATING CIRCUIT BREAKERS CAPACITY IN MOTOR APPLICATION??
what is the advantage of Cathodic eathing system and what is the basic principle and how itis working, please explain clearly .
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
What will happen if we give transformer a dc not ac
how the phase convertor changes the no. of phases
Difference between on line capacitor and Station type capacitor
what is difference between low voltage and high voltage
Why do we need ring main unit (RMU). what is its purpose and its advantages . what is the operating function of rmu
why we use to transmit the power in three phases intead of single phase ?
Can we inject more current in ct primary paralleling 2 loading transformers/Injection kit at a time?let ct ratio be (5000/1A)(per kit rating 2000A range),i need to inject 5000A,if this cant b done means wat is d optional?
in case of transformer the power factor is depend on input or the output
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)