Answer / hardik vyas
TAN Delta test gives you the condition of the insulation
and also it helps in predicting that how long this
equipment can be in service. In short it gives you the
detoriation rate of insulation so you can predict the
remaining useful period of perticular euipment.
Is This Answer Correct ? | 56 Yes | 4 No |
Answer / ashish barak
when insulation is perfect , there is only capacitive
current and angle between current and voltage is 90 degree.
as insulation degrades with time there is a flow of
resitive current also. the angle between capacitave and
resultant current(sum of resitive current and capacitive
current)is this "delta" angle.
as it keeps on increasing it indicates winding is
deterioating
Is This Answer Correct ? | 26 Yes | 1 No |
Answer / swati patkar
for checking transformer bushing insulation so that the life of transformer can be predicted and maintenance and replacement should be done timely.
Is This Answer Correct ? | 1 Yes | 1 No |
design a LV scheme for a 15 storied building?
I have been using an 600VA with 0.6 p.f UPS with my desktop which has 450W power supply unit. Can anyone explain how can this happen . Because the output of the UPS is 360W (600*0.6) (<450W)
why fuse amperes rating are specified ratings like 32amp & 64 amps?
How to calculate per unit impedance of transformer?
how many percent setting of motor over load relay of its full load current
why not phase to phase fault occure in raining day in hv sub-station?
Why current transformers are rated in BURDEN instead of VA?
as we know that N=120f/P speed of an im can be controled only through changing no if poles, can we control by changing the frequncy????
How can we increase the capacity of exixting capacitor bank??????????????? PLS. Help
What is substation?
What will happen if 40W and 60W Bulb is Connected in Series.
What are the loading factors to be considered for transformer sizing/selection?