after parallaing two generators current is shooting up in
both the generators.for ex: load is 400 kw..after paralling
and load sharing current in running gen is approx 900 amps
and incoming is 750 amps which is too high when trying
toshift the load current in incoming gen is coming more
than 1300 amps and both getting tripped and making
blackout..
Answers were Sorted based on User's Feedback
Answer / raj
Is both generator parallel to GRID means Your generator
AVR is not working properly, these requrired kvar sharing
must is there available or not If availabel AVR settings to
shoule be change then is not solved the problem it is
required winding test required.
| Is This Answer Correct ? | 1 Yes | 0 No |
it looks like one of the genset is having a big difference in voltage or
the droop kit if fitted something wrong with it or
check after paralling do you have balanced three phase voltage and current or one of the phase is open circuit or
the gen is running the other as motor
if you know the actual reasons later please let us know also
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / yuvi
This means that the phase angle of the existing generator
and the new incomming generator are not matching. You can
try the bright lamp or the dark lamp method to synk them.
There is no way in which you can directly plug in a
alternator to an active AC system.
| Is This Answer Correct ? | 1 Yes | 1 No |
why the autotransformer burnt while stating the pumpmotor?, In starter and motor there was no abnormality.
why we use iron corn in transformer instead of wooden core
why nutral and earthing wire connect with each other in main panel board.?
Trafo ratio is 11kV/6.6kv,Vector group is YND11. What will be the effect if secondary is used for earthed system.
Why dose voltage rated at 11kva
1 Answers TK Chemical Complex,
What is AVR in Generators and How is it working.
How to check the LM324 Ic
State superposition theorem?
Explain the method to keep noises low in a control system?
power factor is max for which welding a.arc b.resistance c.gas
Classify the different types of load.
why power dissipation is due to low frequency?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)