after parallaing two generators current is shooting up in
both the generators.for ex: load is 400 kw..after paralling
and load sharing current in running gen is approx 900 amps
and incoming is 750 amps which is too high when trying
toshift the load current in incoming gen is coming more
than 1300 amps and both getting tripped and making
blackout..
Answers were Sorted based on User's Feedback
Answer / raj
Is both generator parallel to GRID means Your generator
AVR is not working properly, these requrired kvar sharing
must is there available or not If availabel AVR settings to
shoule be change then is not solved the problem it is
required winding test required.
| Is This Answer Correct ? | 1 Yes | 0 No |
it looks like one of the genset is having a big difference in voltage or
the droop kit if fitted something wrong with it or
check after paralling do you have balanced three phase voltage and current or one of the phase is open circuit or
the gen is running the other as motor
if you know the actual reasons later please let us know also
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / yuvi
This means that the phase angle of the existing generator
and the new incomming generator are not matching. You can
try the bright lamp or the dark lamp method to synk them.
There is no way in which you can directly plug in a
alternator to an active AC system.
| Is This Answer Correct ? | 1 Yes | 1 No |
How can we calculate the motor frame sizes?
What is application of isolation transformer & How it works.
What is thresh hold value of current?
How to select a contactor? How many types of contactors are available
why we generate transmit and distribute electrical supply in multiple of 11
how to compare with Relay settings for HT< panels, RMU panel, and PSS CSS transformer?? 1) Load amps, 2)Tripping time, 3) CT ratio, 4)Cable size 5) Transformer KVA rating 6) transformer full load amps
Electrical 'C' license full abbreviation , and full form
why power factor laggs and leads in case of inductance and capacitance??
PLEASE TELL ME ABOUT QUESTION PAPER OF UPCL ENTERENCE EXAM.
When we giving the 3 phase supply to ups system how to coming netural?
0 Answers Juniper Networks, Tata Motors,
A 15 kw squirrel cage motor having a maximum efficiency of 90% on a continuous full load has temperature rise of 42 degrees celcius after 30 min and 52 degrees celcius after 1 hr under the above operation conditions. a) calculate its final steady state temperature rise on continuous load and the heating time constatnt. b) if the motor is operated on a short load for 9 min estimate its temperature rise. c) calculate the maximum overload that can be applied on a short, 9 min rating so that the temperature rise is the same as the final steady state temperature rise on continuous load.
what are the types of starter ?
25 Answers Andhra Sugars, Bhel, Eveready, HyFun Foods, Jindal, ME, Valeo Lighting Systems India Private Limited,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)