Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


after parallaing two generators current is shooting up in
both the generators.for ex: load is 400 kw..after paralling
and load sharing current in running gen is approx 900 amps
and incoming is 750 amps which is too high when trying
toshift the load current in incoming gen is coming more
than 1300 amps and both getting tripped and making
blackout..

Answers were Sorted based on User's Feedback



after parallaing two generators current is shooting up in both the generators.for ex: load is 400 ..

Answer / raj

Is both generator parallel to GRID means Your generator
AVR is not working properly, these requrired kvar sharing
must is there available or not If availabel AVR settings to
shoule be change then is not solved the problem it is
required winding test required.

Is This Answer Correct ?    1 Yes 0 No

after parallaing two generators current is shooting up in both the generators.for ex: load is 400 ..

Answer / pillay

it looks like one of the genset is having a big difference in voltage or
the droop kit if fitted something wrong with it or
check after paralling do you have balanced three phase voltage and current or one of the phase is open circuit or
the gen is running the other as motor
if you know the actual reasons later please let us know also

Is This Answer Correct ?    1 Yes 0 No

after parallaing two generators current is shooting up in both the generators.for ex: load is 400 ..

Answer / yuvi

This means that the phase angle of the existing generator
and the new incomming generator are not matching. You can
try the bright lamp or the dark lamp method to synk them.
There is no way in which you can directly plug in a
alternator to an active AC system.

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

why the autotransformer burnt while stating the pumpmotor?, In starter and motor there was no abnormality.

4 Answers  


why we use iron corn in transformer instead of wooden core

12 Answers  


why nutral and earthing wire connect with each other in main panel board.?

2 Answers  


Trafo ratio is 11kV/6.6kv,Vector group is YND11. What will be the effect if secondary is used for earthed system.

0 Answers  


Why dose voltage rated at 11kva

1 Answers   TK Chemical Complex,


What is AVR in Generators and How is it working.

4 Answers  


How to check the LM324 Ic

0 Answers  


State superposition theorem?

0 Answers  


Explain the method to keep noises low in a control system?

0 Answers   HPCL,


power factor is max for which welding a.arc b.resistance c.gas

2 Answers   Bhel, HCL,


Classify the different types of load.

6 Answers  


why power dissipation is due to low frequency?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)