why the autotransformer burnt while stating the pumpmotor?,
In starter and motor there was no abnormality.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Autotransformer is for starting of large motor.If you use a
starter additionally ,it requires a certain minimum voltage
for the hold coil.As this voltage was high enough for heavy
starting current which burnt the autotransformer.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / amit kumar singh
The one reason may be that at the time of starting,
induction motor sucts very high inrush current for the
establishment of magnetic field. Thus the total MVA
requirement at the time of motor starting is about 6 to 7
times the rated MVA of motor (if voltage is considered to
remain constant at the time of starting).
As, a transformer can only withstand 1.5 times its rated
MVA (i.e. also only for short duration), the heavy
requirement of MVA by motor could have damaged the
transformer (in case of failure of tap changer operation to
reduce voltage applied before starting of motor).
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / d.lakshmi narayana
To check the transformer tap voltage
persantage.(or)Unbalance the tap voltage (or)To take proper
tap voltage for motor starting load
| Is This Answer Correct ? | 1 Yes | 1 No |
considering the 3phase and single phase ac system the load applied and the volage given is same...will the current differs for both the cases are it wil remain same?
what is 6 pulse and 12 pulse inverter? Explain brifly
What is the meaning of loop in transformer
What do we use in Motor core laminations..???CRGO or CRNGO..and why..????
What is the reasonable voltage between Neutral & Earth of an electrical system for good earthing?
PRV (Pressure relief valve) Trip with oil splash outside power transformers
what happen ehen synchronisation is done at below rated speed
some meggers have three terminals. wat is the real function of the earth terminal?
How to calculate capacitor bank value to maintain unity power factor with some suitable example?
what is the transmission loss for electrical supply? specifically a large shopping complex where the grid is half KM away, what will the % of transmission loss? is there any transmission loss for captive unit generation for above set? thanks
How does cost of generation from hydropower plant compare with other sources of electricity?
Why does curving the pole faces in a dc machine contributes to a smoother dc output voltage from it?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)