How we can design a cable for a 3phase load.
Answers were Sorted based on User's Feedback
Theory
From Ohms law, the voltage drop in an electrical conductor
is
V = I R
where
I = Current, amps
R = Resistance, Ohms
The electrical resistance can be derived from the
properties of the conductor material.
R = ρ L / A
where
ρ = Resistivity, Ω mm2 /m
L = Length, m
A = Cross sectional area, mm2
Watch the units in the above equation.
The resistance can also be expressed in terms of the
material conductivity (ψ) which is just the reciprocal of
the resistivity.
R = L / (ψ A)
Table 1. Typical material electrical conductivity
Material Conductivity, ψ
Copper 58
Aluminium 36
Mild Steel 7.7
Combining Ohms law with the resistance expression, we get.
V = (I L) / (ψ A)
Now, we can define an acceptable voltage drop in a
conductor. I have calculated the voltage drop that was
used in several published tables and get around 5.5 Volts.
We could therefore re-arrange this equation to give the
cable size. But cables come in standard sizes measured in
mm2. In addition, you also need to consider the maximum
current for each cable size.
Table 2. Conductor sizes and maximum currents
Cable Size, mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150
185 240 300
Maximum current, A 13 21 28 36 46 61 81 99 125 160 195 220
250 285 340 395
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / vinothbabu.k
genraly cable slection was based on Rated load amps,voltage
drop,& fault current.
cable which can carry the 1.5 times of the rated amps,cable
shall be consider..
| Is This Answer Correct ? | 2 Yes | 1 No |
How CT & PT ratings are decided for a 11KV or 33KV transmission line?
what is feed back and what are feed back amplifiers?
What is the de rating factor of cable? What is the importance of the de rating factor in cable selection?
How to calculate Busbar Thickness for Different type of HT/LT panels
IS there any special instructions to be taken while installing the tranformer.
WHAT WOULD BE THE FORMULA OF WIRE GAUGE FOR A FULL LOAD CURRENT
How the real power output is controlled in a Generator?
What is a current transformer?
Control cables in S's will carry 1000v which is AC R DC? Pls answer me
Is KCL applicable for close circuit?
I have a 1000 kVA Transformer(11kV/0.415kV) and a APFC panel of 400 kVAR(LT).Now if i want to remove the LT APFC panel and install a HT(11kV) APFC panel on the HT side is the HT APFC panel will work same as the LT APFC panel(improve the power factor),if yes what will be rating of the HT APFC panel?what is the formula to calculate HT APFC panel rating???
difference between power surge and switching transient
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)