Theory
From Ohms law, the voltage drop in an electrical conductor
is
V = I R
where
I = Current, amps
R = Resistance, Ohms
The electrical resistance can be derived from the
properties of the conductor material.
R = ρ L / A
where
ρ = Resistivity, Ω mm2 /m
L = Length, m
A = Cross sectional area, mm2
Watch the units in the above equation.
The resistance can also be expressed in terms of the
material conductivity (ψ) which is just the reciprocal of
the resistivity.
R = L / (ψ A)
Table 1. Typical material electrical conductivity
Material Conductivity, ψ
Copper 58
Aluminium 36
Mild Steel 7.7
Combining Ohms law with the resistance expression, we get.
V = (I L) / (ψ A)
Now, we can define an acceptable voltage drop in a
conductor. I have calculated the voltage drop that was
used in several published tables and get around 5.5 Volts.
We could therefore re-arrange this equation to give the
cable size. But cables come in standard sizes measured in
mm2. In addition, you also need to consider the maximum
current for each cable size.
Table 2. Conductor sizes and maximum currents
Cable Size, mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150
185 240 300
Maximum current, A 13 21 28 36 46 61 81 99 125 160 195 220
250 285 340 395
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / vinothbabu.k
genraly cable slection was based on Rated load amps,voltage
drop,& fault current.
cable which can carry the 1.5 times of the rated amps,cable
shall be consider..
| Is This Answer Correct ? | 2 Yes | 1 No |
what do you know about electrical
How to protect the water pump by no load running.
If one d.g. is unable to take full load of system, then second d.g. will take care of partly Load.for this condition RPM of both DG set should be equal.By using Synchronization panel RPM of dg sets are match, is it true?
in a three pin socket y the pin of earthng is longer n bigger...?
draw the full wave and half wave circuit of 3 phase system and inverter circuit used in ups
placing earthing pit in pathway is correct or wrong??. placing earthing wireGI1/18 inside walls is correct or wrong?. explain!!!
Pls explain about full theory of salient pole generator?
what is the differnce of STATIC ENERGY METER FROM ordinary energy meter?
How we detect the leakage current of 11 KV H.T. motors and waht is the maximim limit?
A 3 phase motor operating off 415V system is developing 20Kw at an efficiency of 0.77 and power factor of 0.73. determine:- a)the line current. b)the phase current if winding are delta connected. c)the phase voltage if winding are star connected.
how we test a 3 phase motor on single phase supply....? HOW WE RUN A 3 PHASE MOTOR ON SNIGLE PHASE. supply for testing..? how we verify of a 3 phase motors 6 wire & name thame a1/a2/a3..b1/b2/b3 and c1/c2/c3 for connecting star delta starter ........i have only 1 phase supply ? help forum..........
how to match 0 -10V with 4 - 20mA
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)