let call Irestrain as Itot, because different relay have different characteristic to define Ires.
for micom P54x, Itot =(|I1|+|I2|)/2,
for sepam T87, Itot =Max(|I1|,|I2|)
where I1=primary current
I2=secondary current,
it need to be consider to calculate transformer ratio factor
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / raghavendran.r
It requires the HT and LT side current ratings to be calculated.The current on the HT side comes around 606A(line current) and on the LT side it is 1818 A(line current), Considering that HT and LT are Delta and Star type wounded respectively.
But for Merz-Prize protection, the CT on Delta side should be Star wound and for the CT on the Star side of Power Trans,it should be delta Wound.
So calculating the primary currents of the CT1 and CT2 we get 350A and 1818A respectively.
Now we have a standard CT ratio of 400/5A and 2000/5A in the market.Which can be used here.
Now the formula for Operating current is mod[Is1 - Is2] = K[Is1+Is2]/2 = K * Iavg.Where K = .1 a constant.
| Is This Answer Correct ? | 1 Yes | 1 No |
What is the meaning of transformer 16 / 20 mva.
WHAT IS THE DIFFERENCE BETWEEN A DC MACHINE OUTPUT AND RECTIFIER OUTPUT...
how to calulate bearing number of any motor ?
What is notching in dc machine?
why we use star and delta connection?why we donot give the supply directly?
12 Answers Hitech, Siemens, Tata Steel Limited,
What will happen if v use DCP Type Fire Exingusher on a Server Chaisis???
what phase and neutral.
why moisture formation found in XLPE Armoured cable outer sheath
What are the causes of motor vibration?
IN 6.6KV 3 phase switch gear .i will give 6.6kv to R phase only to earth in during H.v testing (through H.v KIT).what happen remaining phases.how much voltage get remaining phases.why? explain.
How one can check the faulty capacitor, diode when connected in the circuit ? and when you can not take them out ?
why does chattering take place in ac contactors? can it be avoided & what care does the manufacturer take to eliminate this phenomenon????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)