Answer / mohamed ali
Dear there are use the Formula
I= KVA X 1000/1.732 X 440 X 0.8
100 % - 1669 Amps
80 % - 1335 Amps
So always put in Amps 80% mean 1335 Amps
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / mohamed ali.m
Dear there are use the Formula
I= KVA X 1000/1.732 X 415
For Example
1200KVA
1200x1000/1.732x415= 1669.4 ( Full load Amps
= 1335.5 ( 80% Load Amps)
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / a.bala
As per manufacture recommendation 80 % load can be
possible in continious operation mode . APPX 1300A
or
/ day hour basis u can load up to 100 % APPX 1700 A
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / deepak tyagi
KVAX1000= 440XIX1.732
I=1200,000/440X1.732
I=1574 AMP.
WE CAN DRAW THE MAX. CURRENT 1574 AMP.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vijay
hey guys i think it depends on the power factor
if it is 0.9 then 1200kva*0.9=1080 kw
if it is 0.8 then 1200kva*0.8=960 kw
now you can use your formula
p=sqrt3*V*I*Cosphi watts
I=P/sqrt3*V*Cosphi amps
I=(1080/sqrt3*440*0.9)*1000=1576 amps for 0.9 pf
I=(960/sqrt3*440*0.9)*1000=1401 amps for 0.8 pf
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vijayakrishnan
KW= KVA X PF
please don't include the P.F
I = KVAX1000/1.732XV
I=1200X1000/1.732X415
I=1669.49
now we will be take only 80%
so we take 1335A only
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / nikhil shinde
assume, pf=0.8
then
1200*0.8=960 KVA
I=kw*10^3/1.732*v
=1335.55 @100%
=1068.44 @80%
Is This Answer Correct ? | 0 Yes | 2 No |
HOW TO CALCULATE THE APFC Panel Design
what is the kva rating of 20 kv transformer?
what is G.O.D.S. ?
How can find thermal state value in relay for calculate thermal overload.
What happen if 200KVAR capacitor continuesly connected to load and all the plant machinaries are not in working?
What is AMF Panel????
How to calculate VCB current rating for 2000 KVA transformer
1 Answers Yamuna Power and Infrastructure Ltd,
WHY MOSTLY Rph IS USED FOR CONTROL CIRCUITS AUX. SUPPLY ?
What is the difference in calculating size of AC cables compared to calculating size of DC Cables? Usually DC Cables are larger than AC Cables although they have the same ampacity. Why is it?
where used of HVDS system.
Transformer how to maintaince a check b check c check d check
a wire in which bulb is connected there is two terminal when one terminal is connected to phase than why the value of current shock in nutral terminal is max. or large??