Answer / raju jeyaprakash
LT current = HT Voltage x HT Current/LT Voltage
Is This Answer Correct ? | 14 Yes | 0 No |
Answer / guna
consider T/F rating is 630 KVA
Formula for LT side current(I) = P/1.732*system voltage on LT
side , here P nothing but Load i.e 630 KVA
Is This Answer Correct ? | 4 Yes | 1 No |