A motor works on 30 killo watts.how much ampers will be
required if it works on 440volts?
Answer Posted / gaurang
We Know the Power Equation
P=1.732*V*I*Cosphi
So As per Details
P=30 KW
V=440 Volts
Then,
I=30 KW/1.732*440*0.8
Wher Cos phi=0.8
I=49 A
| Is This Answer Correct ? | 5 Yes | 2 No |
Post New Answer View All Answers
1. A 380 / 220 V r.m.s. 3-phase 4-wire circuit carries loads of 8 + j8.1 ohm; 4 + j4.1 ohm; and 2 +j2.1 ohmin the three phases respectively. The length of the circuit is 100 m, and the resistivity of the phase conductors is 0.0005 Ω/m. The neutral conductor is of the same size as the phase conductors. a) Select a reference angle 0for the first phase. Then write down the three phase voltages in both polar format and complex number format. b) Make appropriate assumptions, and take temperature effects on resistance is insignificant. Calculate the currents in the three phases. (Note: Determine conductor resistance, and apply Kirchhoff’s Voltage Law) Based on the result, suggest a main switch rating for the circuit. c) Show your preferred direction of neutral current in a diagram, and then determine its value. (Note: Apply superposition principle, and Kirchhoff’s Current Law) Use its magnitude to show that in this circuit, the unbalanced load may increase the voltage drop in some of the phases. (Note: Also observe the common volt drip in neutral) State your assumptions, if there are any. d) Suddenly the neutral wire of the circuit is broken. Estimate the new currents in the first phase, i.e. Phase L1. State your assumptions, if there are any.
Is it possible to use a S1 duty class motor for crane application (S4)? If not, why?
in 132kv substation CRT means
my name is venkat .i have good percentage in my academics(ssc 86, intermediate 83 b.tech 73) my question 1..after completion of my ssc i joined in bpc but i didnt got rank in emcet so i completed MPC in one year compartmentally ..so here what am expect question from this background?
what is conductor copnstant of ab cable
What are capacitive,resistive,inductive surge absorbation? What is ferranti surge absorber? What is lagrangian cost? What is Px operator?
what's the requirement of Dy11d0 connection of 3 phase transformer?what's use of it?
what heppend if we are connected u1-v1-w1 as a star point in the place of u2-v2-w2 in power genration
how can you size an automatic voltage regulator?
how to calculate compresor capacity?
Name one of major transformer company in KSA ?
2. What are the parameters of EHT sub-station?
Define maximum demand?
Define relative stability.
What is time response of the control system?