Is MV canble armour can be earthed at both ends?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
No. The pd between the ends may cause current circulating in
the armour resulting in heating.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
If you measure voltage in armour when not earthed ,you
notice the same voltage of the conductor.As there is drop in
voltage in the conductor resulting in pd between the ends,if
the armour is earthed at both the ends the earth closes the
circuit and there will be a small circulating current
through armour also .
| Is This Answer Correct ? | 0 Yes | 0 No |
WHY LINK NOT A FUSE IN AC CIRCUIT
In a 11KV 3phase system do you need to earth both sides of the cable?
difference between brush less & brush excitation in a generator?
how can see the ac indoor or out door ac which Tr
why DC current not used in Transformer action?
17 Answers Engineers India Limited,
why do fans generally rotate in anti clock wise direction??
Graphs of measuring power and speed on dc motor
what is the stear deltaprinceple?
what the different between earthing and grounding?
Write the force balance equation of m ideal mass element.
As per principle we say in three phase supply ,the voltage is producing by phase angle between two phase so two phase is needed means then why we using three phase ?
Why armour HT XLPE power cable required to Earth?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)