Is MV canble armour can be earthed at both ends?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
No. The pd between the ends may cause current circulating in
the armour resulting in heating.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
If you measure voltage in armour when not earthed ,you
notice the same voltage of the conductor.As there is drop in
voltage in the conductor resulting in pd between the ends,if
the armour is earthed at both the ends the earth closes the
circuit and there will be a small circulating current
through armour also .
| Is This Answer Correct ? | 0 Yes | 0 No |
how flow current in 220 kv line to line
where would be tap changer in transformer & why?
If rotor works in clock wise what happens
What will hapen if we run generator below 47.6hz frequency?
why DG battery blast
wat is the importance of reactive power in power generation.....if it is zero means wat will happen to system........
what's the difference between 'shaft power demand' and 'BHP' , when we consider electrical load list.
How is operate breaker failure scheme in substation
What is basic impulse insulation level? And how it is calculated for sub- station?
What are the electrical engineer roles and responsibilities in chemical plant?
when turbine trips generator will becomes induction motor or synchronous motor?
Why infinite busbar has zero resistance and high mechanical inertia?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)