Is MV canble armour can be earthed at both ends?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
No. The pd between the ends may cause current circulating in
the armour resulting in heating.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
If you measure voltage in armour when not earthed ,you
notice the same voltage of the conductor.As there is drop in
voltage in the conductor resulting in pd between the ends,if
the armour is earthed at both the ends the earth closes the
circuit and there will be a small circulating current
through armour also .
Is This Answer Correct ? | 0 Yes | 0 No |
why effective resistance should be more than static resistance in transmission line?
what is the EMF
Hi Recently I got one formula that is Impedence of Xformer = Rated KVA/Root 3 * secondry voltage OF Xformer. Is it Right??????
What are the methods/types of distance protection schemes used in transmission system?
what is the difference between delta delta and star delta connection transformer? why we use delta delta transformer since it need earthing transformer for grounding?
What is the difference between a verilog task and a verilog function?
why insulators colour is BROWN?
why transformer does not obey ohms low?
how mach PF mainten in DG
A simple Question from all.... If Voltage drops then its rated value what will be effect on a Residential load? similarly if voltage rises from its rated value then what will be effects on a load? i know if voltage drops the equipment or device draws more current then its rated what are other reasons ? thanks in advance for ur time.......
What is the difference between PS & metering CT (5p20,0.5 etc.)? Why in PS class CT only Vk is given ? Is PS class CT is more accurate than metering CT?
motor and transformer working with same principle so why motor rotor was roted and transformer not roted