A motor works on 30kw.it is working on 440volts.How much
amper will be Required?
Answers were Sorted based on User's Feedback
Answer / a.bala
Hai Ramya
The formula for I= KW/ 1.732x pf x Applied voltage in kv
So
KW =30
pf=0.8
Applied voltage = 440 v =440/1000=.440
30/ 1.732x0.8x.440=49.2 A
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / dinesh raj
Voltage =440 V
Power Facter (cos@) = 0.8
Power P = 30kW = 30000W
Formula for 3phase power P = sqr(3)*V*I*cos@
So Current I = P/sqr(3)*V*cos@
I = 30000/1.732*440*0.8
So Required amper = 49.2 A
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / a.bala
30 / Rt3xpfx voltage i KV
30/Rt3 x.8x.440= 49.2 A
Consider starter current 1.2 Time from running current
so 49.2 * 1.2= 59 A
sO you will selecte cable and breaker for 60 A.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / sidhu.k
Mr, bala your answer is correct i dont repeat it
again,thank you, i think ramyas dout is clear.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ramendra shukla
Hi Dinesh you are correct but you have made a mistake- in
place of sqr(3) there will be root squre(3)
so Power,P = under root(3) VI Cos@
or P = 1.732 VI cos@
then you are correct while your calculation are correct.
Is This Answer Correct ? | 0 Yes | 2 No |
yesterday i am using my laptop by plugging power supply also battery was working properly after while i unplugged AC power source ,using my battery i played car game (use much power) after that the battery finished the charge and it closed my PC. after that my battery not charge (when unplug automatically PC will turn off)
how does an energy meter works?
Classify driling machines.
Grounding. Dear all at one of my site we checked the amps at the earthing cable to the alternator it was found 125 to 130 A. at the neutal cable in same machine found 146A. in the same plant checked the earthing current on other alternator it was 52A, and neutral 116 A. we are facing problems with our controller and the card was damaged once. can that neutral/GND current be a reason? as there is common grounding for the Alternator,Brkr panel,Transformer?
In a running D.G set engine and Alternator is revolving at 1500RPM but no output in the terminal>>>>what to do?? someone told excitation problem ....please advice
what are the values to be accepted on 3 core 185sq mm for 11000volts on insulation resistance between conductors and between conductors and earthed?
which is better to use svc or synchronous condenser why ?
What do you mean by nominal ratio of instrument transformer?
will there be any problem by recovering slip from single phase induction motors?
why it is unable to birds to be on a 220kV 0r 132 kv lines like on 33kV and 11kV lines?
4 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
why the weight of oil in transformer is specified (on the nameplate) in litres as well as kilo grams?
When we connect the large capacitor bank in series ?