A motor works on 30kw.it is working on 440volts.How much
amper will be Required?
Answer Posted / dinesh raj
Voltage =440 V
Power Facter (cos@) = 0.8
Power P = 30kW = 30000W
Formula for 3phase power P = sqr(3)*V*I*cos@
So Current I = P/sqr(3)*V*cos@
I = 30000/1.732*440*0.8
So Required amper = 49.2 A
Is This Answer Correct ? | 6 Yes | 0 No |
Post New Answer View All Answers
State thevenintheorem?
What is force on parallel conductors ?
What are the different types of hydro schemes?
there are cam operated switches - why we call cam operated , What is cam ?
A cable with concentric PE conductor must be used with frequency converter circuits what does its means.?
If more than rated DC voltage appears across trip coil of the breaker, what will happen? e.g. in 110V DC circuit system, if voltage across battery terminal showing 121 V
Assuming that a dedicated neutral earthing transformer is provided for each GT generator, when the two generators are running in parallel, has consideration been given that the earth fault current from one generator stator winding be split between the two neutral earthing transformers? If so, what adverse impact will this have on the operation of the 59N and 27TN devices?
What are the temperature elements?
How to assume answer to electrical questions
What is PQA???Applications........
What is real time power factor control panel(RTPFC)?
What types of high speed CMOS circuits have you designed?
How to select cable the size, what is the parameters use and what is the formulas use for this cable size calculation?
Please tell me the power flow from pmg to main rotor of an alternator (Including AVR unit)?
what is the question paper model for section engineer in RRB