In a house wiring why we are using only one neutral wire and
so many phase wires from the main board, when the load is
common for both wires?
Answers were Sorted based on User's Feedback
Answer / ajayan
Mr Karthik,In the 3 Ph system also we are having one
neutral wire.Neutral wire is the return path for all the
phases even it is single phase or three phase.
Is This Answer Correct ? | 19 Yes | 6 No |
Answer / prasanna raj
The supply which we are receiving in our homes is Single phase supply only since the loads which we use are lesser rating (hardly 6A-8A)& Single phase is sufficient. In case of heavy loads, Three phase supply is required since the higher loads, single phase is not sufficient. Therefore 3 different phases are used in parallel with one Neutral common for 3 phases to complete the circuit path (in case of Star connection). In case of Single phase supply, there will be 1Ph + 1N. So, loads of our homes (ie; Fans, TV, Fridge, Iron Box, Motor etc) are all of Single phase having 2 terminals one for phase & one for neutral. So, for each & every load, we can connect to our supply's phase & neutral. No problem in that. But however, the common terminal(neutral of all loads)has to be grounded finally. Instead, rather than connecting each load P-N to Supply P-N & then Neutral to ground. We can directly connect supply's neutral to ground & supply's phase to load phase terminal, connecting the load neutral terminal to common grounding wire.
Is This Answer Correct ? | 7 Yes | 5 No |
Answer / karthik raman.b
only one phase we r using in house wiring if u have 3 phase connection u will be have 3 phases.....from main board we r distributing the supply to different areas thats why we have many phase wires
Is This Answer Correct ? | 3 Yes | 11 No |
can any one help me out by posting something related to rvnl interview for site engineer electrical.? what is the procedure? what kinda question they ask us? how long the interview goes? and any tips? and any thing you want to share?
Single phase and threephase power calculation
how much load 15kva dg set can bear
how do i convert 22kw to kva
What is negative sequence over voltage element?
for testing busbar (33kv) hi-pot .whether we can apply DC r not.and what is the test volt for that .explain
how hydrogen or helium is a cooling agent for alternator./ generator of big size.
What is the difference between Earth Fault protection & Neutral Protection
I have 12MW gas engine based power plant its running parallel with grid. my problem is When cpp run in island mode(without geb) that time geb transformer power factor is 0.2 lagging. When cpp run with parallel that time power factor is 0.94 lagging So how can i maintain power factor ofgeb transformer in island mode 0.9 lagging?
what is the actual difference betwen constructional details and constructional features?
What is Mvar?how significant is in electrical energy transmission?
what is the formula for hv test for cable and circuit breaker..????