How can we calculate the rating of a transformer suppose if
load is 1000KW?Formula?
Answers were Sorted based on User's Feedback
Answer / anil dhakar
We know that
KVA=KW/POWER
FACTOR. If the
p.f. is not
given we takes
0.85 value of
p.f.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / proshant
We can dtermine the rating of transformer by multiplying the
power that given inreal power with the power facor.If
thepower factor is not given,then we can imagine it as 0.85
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
The pf is not to go below 0.85 and loading factor can be
taken as 0.9 or as low as 0.7 in anticipation of future
load.Then 1000/ 0.85 x o.9 or 0.7 i.e. 1300 KVA or 1700
KVA is the required rating.
Is This Answer Correct ? | 0 Yes | 0 No |
Why we did not feel electric shock in electric train?
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.
why potetial transformer primary ground?
Whether the vacuum contactor requires Short circuit protection?If No,why?
pls tell me function of closing coil of A.C.B.
What are safety device in vcb and acb?
0 Answers IOCL, L Usine Fashion,
WHAT IS ND RELAY AND HOW DOES IT WORK?
What is mimimum di -electric strength value for 33 KV transformer OLTC oil
Why is the starting current high in dc motor?
why did youi choose this career?
two bolbs of 100w and 40w respectively connected in series across a 230v supply.which bolb will glow bright and why?
16 Answers DRDO, PSPCL, Siemens,
What is effect on in zone and out zone fault if CT chosen for phase side is Vk/2<5mA and Neutral side is Vk/2<15mA on REF protection of Transformer